I assume that you are talking about a bladder tank and pressure switch for a pump that you already have.
Most pressure switches are adjustable over a range of 40 to 60 psi shutoff pressure and should meet your needs.
To select the tank, you must first know the GPM rating of the pump at the operating point. The tank should have an actual size in gallons that is 5 times the GPM rating of the pump; although some will go as small as 3 times the GPM rating. The tank should be pre-charged with air to 2 psi LESS than the START pressure of the pressure switch. They usually come with excess air and you must bleed them down to the correct pressure. If they have no air, you must add the air.
The size is based on assuring that the minimum time to fill the tank will be about one minute (the "3 times GPM" size).
You must install a pressure gauge and you will need a "tire gauge" to check the air in the tank.
If it is a submersible pump you will need a relief valve. Most people don't use relief valves with jet pump systems because they can't generate enough pressure to exceed the capability of the tank.
If you have a regulator system such as a Cycle Stop Valve or a "Smart tee" system, the tank can be smaller. Those systems are often sold as a matched package with the tank, or with the pump and tank.