Thread: Sizing a Boiler Expansion Tank

  1. #1
    DIY Member philtrap's Avatar
    Join Date
    Jun 2013
    Location
    Long Island, NY
    Posts
    66

    Question Sizing a Boiler Expansion Tank

    Folks,

    I have a new condensing boiler with a 30 gallon buffer tank and need help sizing an expansion tank since I'm having problems. Here's the info:

    Buffer Tank = 30 Gallons
    Boiler and Piping = 10.6 gallons

    Total water = 40.6 gallons

    Min Boiler Temp = 80F
    Max Boiler Temp = 180F

    Operating Boiler Pressure = 12PSI

    I have a Extrol #30 4.4 Gallon, but the pressure is always above 15PSI and sometime 24 PSI. I'm thinking I need the #60 (7.6 Gallons) since I added the 30 Gallon Buffer Tank which is new. Not sure if this is the problem or it's the PRV, but the addition of 30 Gallons may have put me into the the next size... I checked the system with te main shut off so the PRV wa basically off and the pressure still raised from 12 to 16..

    Any help is appreciated.

    Thanks

  2. #2
    DIY Senior Member zl700's Avatar
    Join Date
    Aug 2009
    Location
    Texas
    Posts
    235

    Default

    12 psi is the cold start pressure. As water heats it expands and presses against the precharged bladder. At full temp of 180 degrees the system will normally be in the low 20's in pressure.
    A bigger tank may drop the upper end 2 PSI at most, but not needed.

    All is good with your system. Don't touch a thing.

    If the pressure didn't increase when heated, you would experience flashing and pump cavitation that you don't want.
    Last edited by zl700; 09-23-2013 at 04:50 PM.
    If Payback is so important to you, why are you not driving a Toyota Corolla?

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    Using the calculator on this page: http://www.watts.com/pages/support/sizing_ET.asp , you need a tank with at least 3.36 total gallons (from 70-190 degrees, the water will expand 1.21g). So, you should be okay. Put your own numbers in, then compare the volumes required with the spec sheet of what you have to confirm.

    And, depending on where the boiler is mounted, and where the burner is, and considering the upper most floor's radiators are just that, near the floor, you may not have 35' of rise. Now, if you have 10' ceilings in your old house, maybe...
    Last edited by jadnashua; 09-24-2013 at 03:42 PM.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    DIY Member philtrap's Avatar
    Join Date
    Jun 2013
    Location
    Long Island, NY
    Posts
    66

    Default

    Thanks guys - One last question... If the system pressure starts cold at 12psi and goes up to 18psi or maybe 21psi once the boiler runs for a while, should the pressure reduce back to 12psi when the system is off for awhile and cold, or is it OK for the system to return to only about 16 psi?

    Thanks

  5. #5
    DIY Member philtrap's Avatar
    Join Date
    Jun 2013
    Location
    Long Island, NY
    Posts
    66

    Default

    bump. Is it OK to run at +/-24 psi and if the system cools should it reduce back to 12psi?

    Thanks,

Similar Threads

  1. Expansion Tank Sizing
    By Schieftain in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 17
    Last Post: 01-14-2013, 04:43 AM
  2. Sizing boiler allowing for future expansion
    By DPJ in forum Boiler Forum
    Replies: 22
    Last Post: 10-15-2012, 11:54 AM
  3. Replies: 15
    Last Post: 06-06-2011, 04:55 AM
  4. Expansion tank sizing
    By rockycmt in forum HVAC Heating & Cooling
    Replies: 4
    Last Post: 10-01-2008, 07:28 AM
  5. Expansion tank sizing
    By king3735 in forum HVAC Heating & Cooling
    Replies: 1
    Last Post: 01-04-2008, 06:05 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •