    Default Pressure switch rapidly goes on and off at cut in and eventually burns out.

    I have a Goulds J10S jet pump connected to a 2500 gallon holding tank, so it always gets water in as long as the tank is at least half full (which it usually is). I have a Square D pressure switch 30/50 psi that also has the emergency cut off in case the water source goes dry; and a Flotec pressure tank set at 28 psi.

    The system initially worked fine, but, it began to trip the emergency cut off. When resetting the pump began to rapidly cut on and off until it finally caught and pressured up. As water was allowed to drain out a nearby hosebib and the pressure decreased it would again power on but with the rapid on and off until if finally caught on and pressured up.

    I have powered off and allowed the tank to drain, and it is light and easily shaken, so it is not water logged and it still shows the 28 lbs. I have also checked the small pressure line that connects the pressure switch to the pump.

    I have already burned out he points in two switches, and put a 3rd one in yesterday and it is trying to do the same thing.

    I would much appreciate any suggestions!

    Thanks,

    Tom L

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,685

    Default

    Where is the switch relative to the pump and the tank? It should be closer to the tank than to the pump and ideally on a tank Tee.

    Calibrate your air pressure gauge to your water pressure gauge. If one or the other is off, the bladder may be bottoming out on the tank. A jet pump needs pressure to make more pressure and if you shave it too close on the precharge, it will do as you described.

  3. #3
    DIY Junior Member Tom Luck's Avatar
    Join Date
    Jun 2013
    Location
    Marble Falls, TX
    Posts
    5

    Default

    Thanks. The switch is actually mounted to the motor part of the pump. It's reads pressure from a small line to the pump housing part of the pump. The pump is mounted on top of the tank. I'm trying to attached pictures, but, I'm not sure I'm doing it correctly. Name:  IMG_3385.jpg
Views: 179
Size:  48.9 KBName:  IMG_3384.jpg
Views: 206
Size:  74.6 KB

  4. #4
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    Second guess. Too much air pressure in the tank. Tire gauge and pressure gauge are reading different numbers.

  5. #5
    DIY Junior Member Tom Luck's Avatar
    Join Date
    Jun 2013
    Location
    Marble Falls, TX
    Posts
    5

    Default

    I did try lowering the charge pressure. It seemed to help at first, but then it went back to the rapid on/off situation. I might try extending the little pressure line that goes into the switch and extending it down to the pipe on the floor closer to the pressure tank (In stead of it going right to the pump housing). What do you think?

    (And thanks to both of you for replying! I have to get this fixed before my gardens dry up!)

  6. #6
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    If letting air out of the tank stopped the rapid cycling, the tank maybe bad. (Water in the air chamber.) But the sensing line for the pressure switch is a long way from the tank the way it is plumbed.

  7. #7
    DIY Junior Member Tom Luck's Avatar
    Join Date
    Jun 2013
    Location
    Marble Falls, TX
    Posts
    5

    Cool

    Lligetfa, thought you'd like to know, your advice proved to be correct! I did move the switch farther away from the pump and closer to the pressure tank and so far, it is working perfectly! I am thrilled, because up to now, I'd fried two switches and tried just about everything. You're the best! And thanks to all who answered!

    Yours,

    Tom L.



    Quote Originally Posted by LLigetfa View Post
    Where is the switch relative to the pump and the tank? It should be closer to the tank than to the pump and ideally on a tank Tee.

    Calibrate your air pressure gauge to your water pressure gauge. If one or the other is off, the bladder may be bottoming out on the tank. A jet pump needs pressure to make more pressure and if you shave it too close on the precharge, it will do as you described.

  8. #8
    DIY Junior Member Tom Luck's Avatar
    Join Date
    Jun 2013
    Location
    Marble Falls, TX
    Posts
    5

    Default

    Forgot to tell you. I didn't just "extend" the pressure sensing line, as I suggested before (the hardware store guy said that wouldn't make any difference. So, I took the sensor line completely off and put a plug where it used to go into the pump housing and then moved the whole switch and mounted it directly to the pvc connected to the bottom of the pressure tank.

Similar Threads

  1. pump burns up
    By jwelectric in forum Pumps and Tanks Well Forum & Blog
    Replies: 0
    Last Post: 04-13-2011, 05:56 AM
  2. Pressure switch cycling rapidly at cut in
    By SWMICH in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 01-11-2009, 05:23 PM
  3. pump cycles rapidly on/off nothing wrong with tank
    By rick21793 in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 11-21-2007, 11:23 AM
  4. Moen Faucet, it works... eventually.
    By DFWGuy62 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 11-01-2006, 05:50 AM
  5. Pumptrol Pessure switch rapidly cuts in/out
    By JWPH in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 03-29-2005, 02:36 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •