    Default Will Air in line effect heat output

    I have have a new installation with 3 zones each fed with their own zone pump. It seems that in the upstairs zone there isn't much heat comming out of the BB even with 160* water. I am thinking tht perhps there is air in the line. I do not hear any noise of water running. I just cleaned all the BB removing dust and dog hair. The BB are in the order of 30-40 years old. Do they tend to loose the ability to raidiate heat with age?

    Tom

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,388

    Default

    If there is any air in the system, it will tend to naturally rise to the highest point(s). The average circulator does not have enough head to pump without water falling down the backside (return) of the loop, so you have to purge all of the air out. If you don't have purge valve(s) upstairs, it can be tedious to get it all out.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Member tom3holer's Avatar
    Join Date
    Mar 2013
    Location
    Cape Cod
    Posts
    40

    Default

    Jim,

    Thank you for the reply. I just cleaned all the BB in the house and on th first floor there were bleedrs but none on the second floor zone. I do not hear any water running and they are warm but not as hot as I think 160* water should be. I do have a clamp on temp meter and will try that and see.


    Tom

  4. #4
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    If you don't have any bleeders or air vents on the top floor, install something there, since the top of the system is by far the most relevant point in the system for purging air.

    With the dust kittens and dog hair out of it there's no reason why copper-pipe fin-tube wouldn't still hit it's day-1 performance numbers at age 100 years.

  5. #5
    DIY Junior Member dapoppa's Avatar
    Join Date
    Jul 2010
    Location
    NJ
    Posts
    9

    Default

    Circulator head is not what gets water to the highest radiation, it's system pressure. Determine the height of the highest BB, divide by 2.31 and add 4. That's the system pressure required. As far as air vents go, if the circ is installed on the supply vs the return, any air in the system will be absorbed and carried back to the boiler where proper air venting will release it from the system.

  6. #6
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,772

    Default

    Quote Originally Posted by dapoppa View Post
    Circulator head is not what gets water to the highest radiation, it's system pressure. Determine the height of the highest BB, divide by 2.31 and add 4. That's the system pressure required. As far as air vents go, if the circ is installed on the supply vs the return, any air in the system will be absorbed and carried back to the boiler where proper air venting will release it from the system.
    Er, what Jim D said. Once the "backslide" on the returnis established, its an easy lift.
    get all the air out; you need a bleeder up top.
    Then again, I'm not a plumber, just a semi-retired fart arounder.
    I am definitely not a pro plumber, but I am a pro crastinator

  7. #7
    DIY Member tom3holer's Avatar
    Join Date
    Mar 2013
    Location
    Cape Cod
    Posts
    40

    Default

    Thanks guys,

    There is no bleeder on the top floor. I will see about correcting that.

    Tom

  8. #8
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,388

    Default

    FWIW, most installed circulator pumps do not have enough head to push water up a couple of floors until all of the air is out of the system. The ability to generate high head also means higher power, and the goal is often to minimize the power and moderate the flow rate. If the system needs it, then yes, a big enough pump can be specified, but in a residential system, that shouldn't happen too often. A smaller, slower, lower power circulator is also quieter, and is often all that's needed, but you have to get all of the air out, or it won't circulate!
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  9. #9
    In the Trades LamdaPro200's Avatar
    Join Date
    May 2013
    Location
    New York
    Posts
    10

    Default

    A circulator pump does not pump water. It creates a differential. Get air bound, that differential is no longer. 1PSI will lift water 2.31ft. Typical residential heating system maybe 20' from the boiler to the highest radiation. 20/2.31 = 8.66 PSI though the typical boiler feed and exp tank are factory set for 12PSI system.

  10. #10
    DIY Member tom3holer's Avatar
    Join Date
    Mar 2013
    Location
    Cape Cod
    Posts
    40

    Default

    Thank you for the input. I will have to install some bleeders in the upstairs zone.

    I was under the impression that the pump in a closed loop doesn't have to "lift" water as it has the same weight comming down as going up.

    Tom

  11. #11
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,772

    Default

    Quote Originally Posted by tom3holer View Post
    Thank you for the input. I will have to install some bleeders in the upstairs zone.

    I was under the impression that the pump in a closed loop doesn't have to "lift" water as it has the same weight comming down as going up.

    Tom
    Your impression is OK, but with the air up top, there is no water to come down. The water has to "make it over the hill" first, lol.
    I am definitely not a pro plumber, but I am a pro crastinator

Similar Threads

  1. LOW CFM effect and limits on evaporator/AC system ??
    By Jin in forum HVAC Heating & Cooling
    Replies: 10
    Last Post: 08-06-2012, 09:03 AM
  2. Effect of long sweep 90s on a washing machine drain line
    By gpritchett in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 10-02-2010, 10:04 AM
  3. Effect of drain line on plants
    By mwturtle1 in forum Water Softener Forum, problems, installation and reviews
    Replies: 1
    Last Post: 07-24-2010, 07:57 AM
  4. Diverter for shower output OR hand-held output but not both
    By Dgraham in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 07-04-2009, 07:18 PM
  5. Broken Heat Pump Liquid Return Line, Repair or Replace Heat Pump
    By lukekb in forum HVAC Heating & Cooling
    Replies: 4
    Last Post: 06-04-2007, 02:38 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •