Hi all, I just failed a plumbing inspection because we reduced a 2" vent down to 1.5" just before it goes through the roof. We have two vents very close to each other...I'm not sure which fixture's vent we reduced, but I think we did it order to use the old roof jack and not have to deal with a new one. So, it's either the shower vent or the toilet vent.

Can anyone tell me what the required size vents are for those, and if reducing down a vent in general is even allowed?


THANKS!
 

Chetwynd

In the Trades
Messages
45
Reaction score
1
Points
8
Location
California
more details...

Ok, apparently what it is, it's the shower vent, and it's 2" all the way up, and then 1.5" through the roof. I think the inspector was looking at it backwards, thinking the free air coming into the system through the roof was getting reduced, when in fact it's actually getting bigger. Does this make sense? Talk to me guys...
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
What do you have going through the roof on the other vent that passed.
 

Chetwynd

In the Trades
Messages
45
Reaction score
1
Points
8
Location
California
hmmm

Not sure...I think the other one is the toilet and it's 2" all the way up. I mean it shouldn't matter if you go from 2" below the roof to 1.5" above the roof right? 1.5" vent is all thats required for a shower, so as long as 1.5" is going through the roof it should be fine, right?
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
3" through the roof is what is required here so it can't frost up closed and not work.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
This is heresay, but it was my understanding that you would never want to reduce the fitting, and has been mentioned, it is usually enlarged to go through the roof, not reduced. My unprofessional understanding...
 

RioHyde

Plumber
Messages
339
Reaction score
0
Points
0
Location
Cincinnati, Ohio
Your inspector wasnt looking at things backwards. You cannot reduce the size of the vent. Here all vent through roof penetrations must be 3" though this varies in different parts of the country. You need to take it out the roof without reducing it in size.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
It depends on how many total vents through the roof sometimes.

Here, there needs to be a 3" area leaving the building if you have three or less toilets.

That can be:
2-2" vents
1-1.5" vents

A toilet would need the 2"
and the shower could use a 1.5" assuming there are not other fixtures he's looking at and you have your composite somehow.

It's the Seattle area, we don't worry about frost here.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
vent

chetwynd said:
Ok, apparently what it is, it's the shower vent, and it's 2" all the way up, and then 1.5" through the roof. I think the inspector was looking at it backwards, thinking the free air coming into the system through the roof was getting reduced, when in fact it's actually getting bigger. Does this make sense? Talk to me guys...

No. The smallest sized pipe, even if it gets larger lower down, determines the amount of air available, and if it is the one for the toilet it may have to be 2" in your area. Your area may also have a prohibition about reducing the size of a pipe before it passes through the roof. But the discussion is academic, because you have to do whatever he requires, especially if you want the remainder of the project to go smoothly.
 