    Question Help solve an "argument" about a DPST thermostat for my ceiling heat?

    My electrician buddy was admiring my new Honeywell LineVolt Pro 8000 (TL8230A1003) as we prepared to install it. This is a DPST model (two red/two black). I told him I would like to find similar models for my SPST units (One red & one black wire) for my smaller rooms. He said that since I got the thermostat at a great price, I should just do all the rooms with the same DPST model. He said I should simply pigtail both reds and both blacks (Line & Load) and then tie into the existing wiring. I told him this either could NOT be done or it would shorten the life span of the stat. He says I am an idiot. We have a pitcher & pizza riding on it.

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    [QUOTE=Blind Frog;353837. He says I am an idiot. .[/QUOTE]



    Right on!!!!!!!!!!

  3. #3
    DIY Junior Member Blind Frog's Avatar
    Join Date
    Aug 2012
    Location
    Western Ohio
    Posts
    3

    Default

    jimbo - HEY!!! At first I was worried you were saying he was right and I was wrong...then I noticed you are a PLUMBER and not an electrician, so I know you are all wet and your answer can be flushed down the drain!

  4. #4
    DIY Senior Member Chad Schloss's Avatar
    Join Date
    Jun 2010
    Location
    USA
    Posts
    327

    Default

    Check out this image and you surmise who is incorrect
    Attached Images Attached Images  

  5. #5
    DIY Junior Member Blind Frog's Avatar
    Join Date
    Aug 2012
    Location
    Western Ohio
    Posts
    3

    Default

    CRAP!

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,395

    Default

    I do not agree with the drawing of the DPST switch above! A double pole (two paths), single throw (essentially an on/off switch) is commonly used to break BOTH leads of a 240vac device...it is essentially a two pole on/off switch. It is safer since it actually removes power entirely from the device, whereas a SPST switch on a thing like a 240vac heater does stop it from operating, but there's still voltage applied to the device. If it developed an internal short, or you touched something in it and were connected to ground, you could fry yourself. SPDT and DPST are reversed in the drawing.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7
    DIY Senior Member Chad Schloss's Avatar
    Join Date
    Jun 2010
    Location
    USA
    Posts
    327

    Default

    Quote Originally Posted by jadnashua View Post
    I do not agree with the drawing of the DPST switch above! A double pole (two paths), single throw (essentially an on/off switch) is commonly used to break BOTH leads of a 240vac device...it is essentially a two pole on/off switch. It is safer since it actually removes power entirely from the device, whereas a SPST switch on a thing like a 240vac heater does stop it from operating, but there's still voltage applied to the device. If it developed an internal short, or you touched something in it and were connected to ground, you could fry yourself. SPDT and DPST are reversed in the drawing.
    Yep. These look better. Copied that image from google...

    http://www.kpsec.freeuk.com/components/switch.htm

  8. #8
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Quote Originally Posted by Blind Frog View Post
    jimbo - HEY!!! At first I was worried you were saying he was right and I was wrong...then I noticed you are a PLUMBER and not an electrician, so I know you are all wet and your answer can be flushed down the drain!
    I was a Master Chief Electronic Technician in the Navy, couple that with on a submarine everyone learns about everything, I feel eminently qualified to comment on switches!

Similar Threads

  1. Termosyphon system and closed loop copper heat exchanger "dillema"!
    By leaualorin in forum Solar and Geothermal Water Heating Forum
    Replies: 2
    Last Post: 11-27-2011, 02:02 PM
  2. ceiling fan lights "pop" and went dead
    By Ed from chicago in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 08-07-2010, 05:20 PM
  3. "Machine Gun" or "Thud" and a Weeping Toilet...oh my!
    By maxxis in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 03-22-2009, 07:38 PM
  4. water heater "heat loops"
    By edwardh4 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 12-18-2008, 04:08 AM
  5. Difference between "thinset" and "dryset" mortar...?
    By Fistor in forum Remodel Forum & Blog
    Replies: 4
    Last Post: 07-31-2008, 02:44 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •