    Default "Running Water Sound" coming from behind the walls - What could be the cause?

    I was doing a little drywall yesterday on a job site in Down Town Vancouver and received a call from a client in North Vancouver. The call went like this.

    Client: "John, what is the name of your plumber?"

    Me: "I have a few, which one?"

    Client: "The one that worked on our home."

    Me: "Dean, Why?"

    Clinet: "Because we can hear water running behind the wall. _____ shut the water off to the house and the noise stops. Any ideas?"

    Me: "I'll be right over."

    Not what you want to hear. I was sick to mu stomach and raced towards the North Shore Mountains to check our work.

    Here is what I found.

    I could hear the water from under the kitchen sink, the powder room bathroom, the Laundry room, Mechanical room and outside hose tap. I could not hear the sound from the new supply lines my plumber feed the master ensuite.

    To rule out straight away that it was not my plumbers fault or the fault of me or any of my trades I shut down the new ensuite completely. The sound is still there.

    We tried checking the toilets to see if they where running. Nope.

    Checked that the hotwater tank was not leaking. Nope. I even turned off the hot water tank and the sound continues.

    We checked the main water connection to the house and found this.



    The connection and access leaves much to be desired and the shutoffs are under water! WTF

    I scooped out the water was fast as I could with my Slurpee cup and the water level came back within 2 minutes.



    So - if the sounds stops after this connection is turned off is it most likely we have a leak in the original plumbing lines somewhere under the hose or is it safer to say the shut off itself is leaking. My gut thinks this and my plumber is going today to re-check my inspection and replace this shutoff.

    Any other ideas?


    JW


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  2. #2

    Default

    Sounds to me like it could be a pin hole leak in the incoming water line, on the street side, of the house shut off.

  3. #3
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,957
    Blog Entries
    5

    Default

    Quote Originally Posted by Cookie View Post
    Sounds to me like it could be a pin hole leak in the incoming water line, on the street side, of the house shut off.
    Ian checked out the line and found two leaks.

    One leak was a slow trickle through an exterior hose connection and he fixed that and the sound only slowed down a bit. The other leak he is guessing is somewhere in the home.

    My client is not thrilled about removing floor tile and drywall to start the process and is looking into companies that can repipe with other methods.

    5 years ago when the kitchen and laundry room where done they should have replaced the 50 year old water lines. I did not do this reno for them only the master en-suite. What a shame they didn't spend the extra few hundred for new pipe back then.

    JW


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,374

    Default

    It isn't obvious from the pictures what type of piping it is, but if it is galvanized, whomever did that work did them a big disservice by not replacing all that they touched. Now, copper could last a century or more without problems, and depending on water conditions, might outlast the house.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,957
    Blog Entries
    5

    Default

    Jim the piping is copper and the connection from the shut off to the street is Pex. The pex is 10 years old and the copper a good 60 years old.

    JW


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  6. #6
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,957
    Blog Entries
    5

    Default

    I heard from the plumber that my client is looking for a local Vancouver company that can fish a new plumbing line through the old one. Has anyone ever seen this done before?

    What type of gear do you need to do it. I was told that as the new pipe feeds through the old one it breaks it apart. This I got to see in person. If they can re-pipe this home with no drywall repairs or removing floor tile I will be very impressed.

    We'll see.

    JW


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  7. #7
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,374

    Default

    I've heard of this technique for drain lines (works especially well for clay or cement tile pipe), but not for water supply lines. SOme companies can try to use the existing pipe to thread a cable, and use that to pull the whole thing out while pulling in a new one. No experience with either technique. Good luck to them.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  8. #8
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,957
    Blog Entries
    5

    Default

    Quote Originally Posted by jadnashua View Post
    I've heard of this technique for drain lines (works especially well for clay or cement tile pipe), but not for water supply lines. ...
    Me neither. I will have to go and watch if it does turn out it's possible.

    Should know this week what the plan of attack is. I sense a drywall patch job coming. I think we can ripe the three room from the ceiling down. The master is all new piping so then the whole place is up to date.

    JW


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  9. #9
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    I've seen it done. Can't recall all the details.
    It was soft copper if I recall and I was blown away at the efficiency of how it was done.....
    The only deets I remember was prep....turn off street main, pull new line in and before the day was even over, water was back on with a new main

  10. #10
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,957
    Blog Entries
    5

    Default

    Quote Originally Posted by chefwong View Post
    I've seen it done. Can't recall all the details.
    It was soft copper if I recall and I was blown away at the efficiency of how it was done.....
    The only deets I remember was prep....turn off street main, pull new line in and before the day was even over, water was back on with a new main
    Turning the water main off is easy since we have a City Connection right at the sidewalk. How they pull a new pipe through old copper under a floor is something I have got to see. I'll believe it when I see it. Looking forward to seeing a new trade in action!!!

    JW


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  11. #11
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    Ha. I just re-read it as I thought I missed this one detail.
    What I saw was out underground......so no clamps or whatnot holding the pipe in place.

    In your case, methinks the sawzalls are coming out to play ;-)

  12. #12
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,957
    Blog Entries
    5

    Default

    Quote Originally Posted by chefwong View Post
    Ha. I just re-read it as I thought I missed this one detail.
    What I saw was out underground......so no clamps or whatnot holding the pipe in place.

    In your case, methinks the sawzalls are coming out to play ;-)
    That's what I was thinking too. Have you tried using an Fein Tool for this. Amazing how easy you can cut through drywall with limited damage and dust.

    JW


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  13. #13
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    Actually, the 12V sawzall is the perfect tool for this application or Fein. I prefer the 12V - as no cords, up in the air.
    U still need to cut a area large enough to add blocking, etc to get new drywall up.

    And me, being the idealist as I am.....I will often cut out much larger depending on the location of where I'm cutting in order to avoid a butt seam or floated out crown. I'm a stickler for flat so sometimes in order to get flat, you need to remove more rock so it's just all flat rock without butt seams..

  14. #14
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,957
    Blog Entries
    5

    Default

    Quote Originally Posted by chefwong View Post
    Actually, the 12V sawzall is the perfect tool for this application or Fein. I prefer the 12V - as no cords, up in the air.
    U still need to cut a area large enough to add blocking, etc to get new drywall up.

    And me, being the idealist as I am.....I will often cut out much larger depending on the location of where I'm cutting in order to avoid a butt seam or floated out crown. I'm a stickler for flat so sometimes in order to get flat, you need to remove more rock so it's just all flat rock without butt seams..
    12V ? Does your wife know your using her tools? lol Just kidding.

    Chef Wong you need to check out this new paperless drywall tape from FibaFuse. If you visit their website you can get a free sample sent to you. It sucks for inside corners but for butt splice repairs it's fantastic. Their website says they sell 36" rolls but I could not get anyone to call me back or sell me some. Since the stuff looks a lot like the Mapei reinforcing fleece for my liquid waterproofing I started testing drywall patches with it. OMG what a product with Joint Compound!

    The Mapei fleece is stronger than the FibaFuse by a long shot and sits down so flat.

    We do a lot of 3-6" hole saw entries in drywall. We re-install the plug and patch.

    Now I can install some blocking, install the plug and cover in one go with a custom size fleece from 0 - 36" wide. This covers the seam and the screws in one go. And - the patches dryout faster than paper tape ones. I'd love some more feedback from others - if anyone wants to try this stuff I'll send out a few samples of my off cuts.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  15. #15
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    Been using the Fiba for along time.....You can use that as the fleece with Hydroband and AquaD....
    It's good stuff. That is the ONLY fiberglass I would use on a patch. The other stuff is just bunk. I still prefer paper moreso for the reason of telepgraphing of joint lines. And you still do need to mud thicker than the original wall and feather out. My ~golden~ eyes do pick up on this, sorta like cornerbeads. I'm a stickler for straight corners. Not feathered out straight corners. In order to do this....I undercut the edges and mud out for No Coat. This gives my the 90's I want versus tapered 90's.

    So yeah, for efficiency for the customer, the patch is surely the way to go. Mostly DIY on my end, so time and labor is my fee....and yeah, I often rip out more just to avoid the ~crown~

    Another theory to share. I like using regular AP mud for patches. As it dries - it compresses (pulling in the tape tighter IMO). Hot mud is great and all but I find it blooms..
    Last edited by chefwong; 07-17-2012 at 08:43 AM.

Similar Threads

  1. Traps in Walls: "Can't" vs. "Shouldn't"
    By speede541 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 03-08-2011, 11:33 AM
  2. "chugging" sound when tank fills
    By blu_ize317 in forum Toilet Forum discussions
    Replies: 0
    Last Post: 02-01-2011, 03:38 PM
  3. Intermittent Low Pressure, "Lagging" Sound Well Pump
    By wcp in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 06-27-2010, 11:01 AM
  4. "cricket" sound after turning off shower
    By mav91 in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 08-18-2009, 06:20 AM
  5. "Oily smell" coming from one hot water tap
    By MikeW888 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 09-15-2008, 02:01 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •