    Default Rough in shower install leaks

    Here is what I've installed.
    Name:  7004400434_993da69cf6.jpg
Views: 1318
Size:  25.1 KB
    Here is what leaks. It's Blue Monster Pipe Thread Sealant.
    Name:  7004397386_dc5f5f1c39.jpg
Views: 440
Size:  87.0 KB
    Only the hot water "in" leaks. but I'm assuming this is not how it's done. I should have probably soldered the fittings after tightening them the best I could?
    Name:  7004400064_a11bb6066b.jpg
Views: 690
Size:  24.4 KB
    If soldering this close to the plastic workings inside do I remove them like I did for the mixing valve?

    Any help/scrutiny/criticism is welcome and much appreciated.

    Thanks,

    Mike

  2. #2
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    I don't suggest trying to solder that threaded connection.

    There is no easy fix for this.

    You need to properly clean and flux any future soldering you do here, and you need to remove the water from the lines.

    Cut it or sweat something loose and get the male adapter tighter.

  3. #3
    DIY Junior Member Rigger33's Avatar
    Join Date
    May 2012
    Location
    Virginia
    Posts
    2

    Default

    Quote Originally Posted by dlarrivee View Post
    I don't suggest trying to solder that threaded connection.

    There is no easy fix for this.

    You need to properly clean and flux any future soldering you do here, and you need to remove the water from the lines.

    Cut it or sweat something loose and get the male adapter tighter.
    Thanks! Didn't think it would be an easy fix. Just wanted to make sure there wasn't some trade secret that may have made this alittle more reassuring. After reading some similar incidents here I think I'll try the "overkill method" with tape then thread sealant.

  4. #4
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    I've always done the tape and dope method on water feeds.
    What always is the issue for me is heating the cup just long enough to get solder to wick in without heating it too long to affect the dope in the threaded end just like yours. I turn on the water and pray there are no leaks when you're working in a tight spot like that where do over is a 23@@!#$$

  5. #5
    DIY Member tom12's Avatar
    Join Date
    Aug 2011
    Location
    California & UK
    Posts
    63

    Default

    As mentioned above, cut/free the cu supplies, and wind-out, clean and remake the adapters - all of them. Wrap tape twice around the threads and then dope them.
    Thread them back in. Before cutting the cu. tubes, clean the area of the cut, it will make it easier when you sweat connectors to re-assemble the rig.

    Never sweat one end of a made/in-situ IPS fitting. Solder on a short stub of cu. before threading an adapter into a body. The stub can be cut to the required length. Always remove the works from a to be soldered valve. Any valve.

  6. #6
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    But in the clearances of the OP valve and , there's not alot of room to solder and the thread the onto the body

  7. #7
    DIY Member tom12's Avatar
    Join Date
    Aug 2011
    Location
    California & UK
    Posts
    63

    Default

    Quote Originally Posted by chefwong View Post
    But in the clearances of the OP valve and , there's not alot of room to solder and the thread the onto the body

    If there's not enough room to spin the adapters out then cut twice, on the straight pipe beyond the 90 and between the 90 and the adapter. Wether the OP uses new material or pulls apart and re-assembles the existing mats. is up to him. AAMOI: i should re-make all five adapters - do it now, not when it later possibly leaks in the wall. I speak as a veteran of quick fixes.

    Another method would be to cover the adapter and valve tapping with a frozen, damp cloth,and sweat the 90 away from the adapter ( wear gloves ) then remake the join as above.. Using this method i should pre-remove all vulnerable works from the valve.

    AAMOI: I shouldn't attempt to sweat the adapter into the valve body, because if it doesn't take then you'll have quite a job merely getting the adapter back out - leave that technique to plumbers.

Similar Threads

  1. New bathroom install help! Rough-in Plumbing
    By dcf1999 in forum Remodel Forum & Blog
    Replies: 0
    Last Post: 03-07-2012, 10:13 AM
  2. Help - Tub / shower install 58.5" rough opening!!!
    By cleaver in forum Shower & bathtub Forum & Blog
    Replies: 10
    Last Post: 02-15-2012, 05:46 AM
  3. Guinevere leaks at base - not a new install
    By willmed in forum Toilet Forum discussions
    Replies: 3
    Last Post: 07-31-2007, 06:40 PM
  4. Rough-In Valve Install
    By Dogman in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 04-06-2007, 10:48 AM
  5. Shower Valve Deep Rough-In kit leaks
    By duners in forum Shower & bathtub Forum & Blog
    Replies: 8
    Last Post: 01-18-2007, 05:58 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •