    Default Pause in water pressure

    Hi,
    I have a submersible pump and your typical currently available pressure tank with a bladder or rubber liner. The pressure seems good and the well is good, but every 5-6 minutes when the water is running it dries up to trickle and then kicks in again back to normal pressure. The dropping and resurgence only lasts about 10 seconds but is a real pain. I have one pressure gauge which is on the line from the well and prior to the pressure tank. This isn't an abrupt situation, it has been a slow progression over the last year or so. Is this a simple pressure cut off adjustment?

    Kim

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    It could be that the air precharge is too high so the tank runs out of reserve before the pump comes on. It could also be a failing pressure switch whereby mineral build-up under the diaphragm is causing the pump to start at progressively lower pressure.

  3. #3
    DIY Junior Member KDickinson's Avatar
    Join Date
    May 2012
    Location
    Ottawa, Canada
    Posts
    3

    Default

    Ok, so if it's the air precharge how do I adjust that? So getting a new switch would solve the second possible issue?

  4. #4
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    There are stickies for replacing a switch and maintaining the bladder tank.

  5. #5
    DIY Junior Member KDickinson's Avatar
    Join Date
    May 2012
    Location
    Ottawa, Canada
    Posts
    3

    Default

    What are average life spans of switches and bladder/captive air tanks?

  6. #6
    DIY Senior Member craigpump's Avatar
    Join Date
    Apr 2012
    Location
    ct
    Posts
    710

    Default

    Shut the power off to your pump, drain the tank, and then check the air pressure in the tank at the air charge valve. The air charge should be 2 psi below cut in pressure, for example if your system operates on a 40/60 pressure differential you should have 38 psi on the tank.
    I have seen good bladder tanks last 25+ years. I replace pressure switches every 5 years and I always use a brass nipple under the pressure switch. Be sure there is a pressure relief valve in the system!

Similar Threads

  1. Water Softener On = No Pressure, Bypass = Normal Pressure?
    By jsarin1 in forum Water Softener Forum, problems, installation and reviews
    Replies: 4
    Last Post: 03-08-2011, 04:06 PM
  2. Could my new pressure balance valve be reducing my water pressure?
    By JenJen in forum Shower & bathtub Forum & Blog
    Replies: 8
    Last Post: 02-22-2011, 06:57 PM
  3. High Water Pressure Spikes on Well with Pressure Tanks
    By RayMan in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 02-01-2010, 12:57 AM
  4. Water in well, pump working, can't build up pressure, but doesn't lose pressure????
    By bgnotaplumber in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 08-20-2007, 10:32 AM
  5. Toto Drake Flush/Fill Pause
    By Jerome in forum Toilet Forum discussions
    Replies: 2
    Last Post: 11-23-2005, 06:49 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •