    Default Using Generator To Power Well Pump

    I have a Goulds Model 7GS05422 well pump. It is referred to as “2 wire” but has 3 wires actually running to it.

    To power the pump using a 240 volt generator, which wires from the generator should be connected to which wires on the pump motor? The generator has a NEMA L14-30 connector.

    Thank you.

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    You should not connect directly to the pump. Connect it to the pressure switch.

  3. #3
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default NEMA L14-30P AC Plug

    Quote Originally Posted by Regis Tration View Post
    I have a Goulds Model 7GS05422 well pump. It is referred to as “2 wire” but has 3 wires actually running to it.

    To power the pump using a 240 volt generator, which wires from the generator should be connected to which wires on the pump motor? The generator has a NEMA L14-30 connector.

    Thank you.
    Connect X & Y to Pressure Control, and G to Ground.

    Name:  6244.jpg
Views: 2017
Size:  10.1 KB

    Be careful playing with electricity.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  4. #4
    DIY Junior Member Regis Tration's Avatar
    Join Date
    Jul 2010
    Location
    Massachusetts
    Posts
    6

    Default

    Thank you.

  5. #5
    DIY Junior Member BrianK's Avatar
    Join Date
    Jun 2012
    Location
    Calgary, Alberta, Canada
    Posts
    26

    Default

    The first 2 wires are L1 and L2 (240 VAC between the two), the 3rd wire may be a ground if it's green or if yellow could be the capacitor start wire. You can tell this if you have a control box near the pressure switch/tank and you have 2 wires from your power panel feeding it and the 3 wires from the pump wired into the control box. If the 3rd wire is a ground, it should be obvious as it will be connected to other ground connections somewhere. As recommended above, the proper place to connect the generator power is where power comes to the pressure switch or a junction box near there (or if you have the control box see where it is fed from and connect it there). When you do that you MUST disconnect the normal or line power otherwise if you still have utility power - BOOM and you will probably wreck your generator. If you don't disconnect your normal/utility feed to the pump and you connect the generator, you will also be powering up your house and the line back to the transformer and ultimately the high voltage power line. This is dangerous to the linesmen trying to fix the power outage. (of course this assumes you have utility power)

  6. #6
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,632

    Default

    Quote Originally Posted by BrianK View Post
    When you do that you MUST disconnect the normal or line power otherwise if you still have utility power - BOOM and you will probably wreck your generator. If you don't disconnect your normal/utility feed to the pump and you connect the generator, you will also be powering up your house and the line back to the transformer and ultimately the high voltage power line. This is dangerous to the linesmen trying to fix the power outage. (of course this assumes you have utility power)
    Good point.

    I assumed it was the only power source.

    Thanks for the Safety precaution. Better to be safe than sorry.


    Be careful playing with electricity, Unless you like a shocking experience.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  7. #7
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,933

    Default

    How many watts is your generator?
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

Similar Threads

  1. power generator
    By bronzemaxell in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 08-30-2011, 06:25 AM
  2. Which Pump and Generator Combination?
    By andyrud in forum Pumps and Tanks Well Forum & Blog
    Replies: 4
    Last Post: 06-01-2011, 11:48 AM
  3. Portable generator and generator panel incompatibility
    By luc in forum Electrical Forum discussion & Blog
    Replies: 16
    Last Post: 05-21-2009, 12:29 PM
  4. Help buying a generator for power outages
    By allycat in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 05-01-2009, 09:55 AM
  5. Running a pump from a generator
    By tmartin in forum Pumps and Tanks Well Forum & Blog
    Replies: 6
    Last Post: 04-24-2008, 06:12 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •