    Someone (sorry, I forget who) posted a link to this very nice compilation of fittings and basic code requirements on a thread. The majority of it I was familiar with, but there were a couple questions that came up as I read through it. Any edumacation you can give would be much appreciated

    Here's the link

    So a SanTee is used for a trap arm. I would assume from this that a double SanTee would be for side by side lavs with the drain/vent in the middle, or do you have to use the double fixture fitting for this application? Is the double SanTee only for joining vents? The double fixture is for back to backs and side by sides... Is this the required fitting, or are they both options? What is the difference in use between these two fittings, and why? Is the sweep/flow just better on the fixture fitting, and the double santee is just an option for venting b/c its shorter?

    You see both combination wye fittings and SanTees being used to connect a horizontal drain into a vertical one. Are both permissible in general, or are there different requirements for each's use? I know you need the SanTee for a trap arm, and the combination wye for horizontal to horizontal drains, but are there other specific differences in a horizontal to vertical drain application, or can either be used?

    On the 2nd Drains and Vents page, it shows a vent under a window and says to use drainage fittings. What is this about?

    In the Sinks section, bottom left pic is a lav draining into a toilet vent, and being vented by it. So you can do this, as long as the trap arm is under 3'6" and you only do it on the same floor? Is that correct?

    Is the distance between trap and vent on 2" line greater than 3'6"? Related to that, what are the specific requirements of flat venting?

    It says that no drains from other fixtures may enter the closet bend, only downstream of the vent. Is this correct? Unless I'm misreading this, I know that my house has inlets on the closet elbow, and wyes coming off the 3" horizontal before the vent in almost every location, and it passed inspection a few years ago. My county adds a lot of extra code requirements in general, so I'd be surprised if they let this fly if its not generally acceptable...


    Ok, that ended up being more questions than I thought. Thanks to anyone who is willing to help me get a more complete understanding of these codes.

  2. #2
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    The double fixture fitting is quite a bit different than a double san-tee.




    The only time I've seen a wye used to tie a horizontal drain into a vertical drain stack is after the fixture has been vented.

  3. #3
    In the Trades mtcummins's Avatar
    Join Date
    Jun 2010
    Location
    Pittsburgh PA
    Posts
    380

    Default

    I can see that it is a different fitting, I guess I'm just asking why its different in use.... does it flow better for 2 trap arms? Why is it so different from a single SanTee?

    Its kind of a moot point for me, we're not allowed to use them in my county, have to split a double sink into 2 drains and 2 vents and join them back together above flood rim (even on a kitchen sink, which requires 2 traps here), but I'm curious what the more normal way of doing things is...

  4. #4
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    For sinks I think it has more to do with trying to snake the line.

    For back to back w/c, a flush on one side can push up into the other w/ san-tee.

  5. #5
    In the Trades mtcummins's Avatar
    Join Date
    Jun 2010
    Location
    Pittsburgh PA
    Posts
    380

    Default

    Ah, those both make good sense. Thanks

  6. #6
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    SanTee is used only on the vertical. And a combo, or wye + 45, is NOT used on the vertical. If it was, the take-off for the vent would be below the weir of the trap, hence the trap would self-siphon.

  7. #7
    In the Trades mtcummins's Avatar
    Join Date
    Jun 2010
    Location
    Pittsburgh PA
    Posts
    380

    Default

    Quote Originally Posted by jimbo View Post
    SanTee is used only on the vertical. And a combo, or wye + 45, is NOT used on the vertical. If it was, the take-off for the vent would be below the weir of the trap, hence the trap would self-siphon.
    Those requirements are for a fitting where you're pulling a vent off right there. I was referring to combining drain lines further down, and other circumstances for the use of those fittings. Is there any rhyme or reason to how to combine two drain lines after the vent, or is either acceptable based on circumstances? I tend to try to use a wye whenever possible (other than for a vertical vent fitting), as it just seems like it would flow better, but are there requirements or best practices regarding a wye vs a tee for combining a horizontal drain into a vertical drain post vent?

    Any input on the other things in my OP?

    Thanks.

Similar Threads

  1. Sharkbite Questions Code Leaks hate em like em
    By yngwie_69 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 43
    Last Post: 01-07-2013, 03:53 PM
  2. Replies: 1
    Last Post: 01-09-2011, 08:13 AM
  3. Misc Residentual Code Questions
    By Master Brian in forum Electrical Forum discussion & Blog
    Replies: 34
    Last Post: 02-02-2009, 08:27 AM
  4. Hot water heater and code questions
    By spebby in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 09-21-2008, 09:03 AM
  5. California code questions - water heaters
    By mikeyvon in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 01-22-2008, 03:12 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •