    Hi
    I'm in the process of renovating my small 1946 bungalow.
    Its a fairly extensive remodel (all the drywall is off) and since I have the opportunity to access most of the plumbing, I'd like to take the opportunity to bring it up to current code if possible.
    I'd appreciate any advice on what should be done to add venting, cleanouts (or anything else) to bring this up to current standards.
    I've added a diagram to show the current layout (in black) along with some of my thoughts on updates (in red).

    Developed lengths of all horizontal branches are less than 1.5m(4.9ft)

    It's originally a single level house that has had a basement suite installed as part of a previous renovation (prior to us buying the house).
    The bathrooms are located one on top of the other and use a basic stack vent waste system.

    The basement drain plumbing is buried beneath the concrete slab so I'm not sure what's going on there but a separate vent stack was added presumably when the downstairs bathroom was put in.

    I'd appreciate any suggestions on additional venting for the lavatories, adding cleanout locations and the use of TY fittings on the main stack.

    thanks in advance for your help
    Jonathan
    Attached Images Attached Images  

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    It's perfect and it works. Leave it alone
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    I have a hard time believing that those lavs both have 2" serving them, and I think those red vents are what hj calls "cosmetic".

  4. #4
    DIY Junior Member jono604's Avatar
    Join Date
    Nov 2011
    Location
    vancouver, BC
    Posts
    11

    Default

    Hi dlarrivee
    Thanks for your response.
    You're partially correct. The basement lav is 1-1/2" (my mistake). The upstairs lav is definitely 2". We installed this section.
    In the upstairs bathroom we installed all new ABS piping but the general layout is the same as the original. We swapped the lav and WC position for a better bathroom layout.
    During the upstairs piping upgrade we upsized the lav drain to 2". The lav will have a 1-1/4" strainer so I'm not sure if 2" is necessary here.
    What do you think?

    When you say the proposed (red) vents are "cosmetic" are you saying they're not needed?
    I certainly don't want to add extra plastic if I don't have to.

    Do you think there's any benefit to the upper cleanout or is it ok to service the upper section of the stack from the bottom cleanout?

    thanks again for your help

    j

  5. #5
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    If everything is indeed within 5' of the stack, I can't see any reason or any benefit to adding those extra vents...

    I'll let a pro chime in here though.

    As far as clean outs, you can have as many as you'd like. Add another one if you have a spot that will be accessible and you're cutting into that stack anyways...

  6. #6
    DIY Junior Member jono604's Avatar
    Join Date
    Nov 2011
    Location
    vancouver, BC
    Posts
    11

    Default

    Yep
    The upstairs lav is the furthest from the stack and is only 4'.
    Hell the whole bathroom is only 8' wide... ;-)

    thanks again for the feedback
    j

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default

    The upper vent and cleanout ARE "cosmetic" and perform no useful purpose. The lower "red" vent is "functional" and should be installed.
    Licensed residential and commercial plumber

  8. #8
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Little has changed in the codes for basic drainage systems. Of course lots of areas were built when there were NO codes in effect, but plumbers often knew to "do it right". It would be a major mistake to replace sanitary tees on the vertical stack with TY's. THAT would violate code AND cause trap problems.

  9. #9
    DIY Junior Member jono604's Avatar
    Join Date
    Nov 2011
    Location
    vancouver, BC
    Posts
    11

    Default

    Thanks hj and jimbo for your comments

    Just for clarification the connections to the stack are all done with sanitary tees. I got my terminology mixed up (I though a TY was a sanitary tee, I now realize a TY is a Y+45)

    So it looks like everything is good to go with the exception of adding a vent to the downstairs lav.
    I'll get on this when we start remodelling the basement

    Thanks everyone for your help. As a first time DIYer it's great to have this type of reassurance.

    j

Similar Threads

  1. Advice needed on updating hot water heater lines.
    By Austin83 in forum Water Heater Forum, Tanks
    Replies: 8
    Last Post: 05-18-2011, 03:18 PM
  2. Updating exsisting plumbing
    By naglejob in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 06-12-2010, 03:01 PM
  3. Advice needed on updating tub/shower fixtures
    By rhosch in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 02-13-2009, 02:50 PM
  4. Help Updating Basement Plumbing Drains
    By djmed in forum Remodel Forum & Blog
    Replies: 0
    Last Post: 01-12-2009, 08:10 AM
  5. need advice on updating boiler system
    By IleanasColors in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 02-20-2007, 07:16 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •