Advice on proposed layout for updating bathroom plumbing

Users who are viewing this thread

Wyeorwyenot

New Member
Messages
3
Reaction score
0
Points
1
Location
Pittsburgh, PA
PXL_20230918_003848000-min.jpg

This picture shows the current bathroom plumbing. The pipe on the left is the sink drain and has a vent pipe on the other side of the bathroom. The abs portion of the plumbing on the right is for the tub. Due to a few factors I need to move the partition wall the tub vent traveled in and move the toilet over a couple inches (yes, I know the joist is in the way).

My proposed layout is below. Any advice, critiques, or confirmation on design would be greatly appreciated. Is it possible to consider the main stack vent appropriate for the tub? The drawing is supposed to be the same point of view as the picture. Sorry for poor drawing!
PXL_20230918_004754078-min.jpg
 

Jeff H Young

In the Trades
Messages
8,954
Reaction score
2,235
Points
113
Location
92346
well its not very clear , but it might work that way hard to interpet . but what fitting are you expecting to get a 2 inch move with toilet? even a spigot 22.5 degree befor the closet bend will give you more than 2 inches
 

Wyeorwyenot

New Member
Messages
3
Reaction score
0
Points
1
Location
Pittsburgh, PA
Well it needs to move about 4 inches, so I was planning a 22.5 degree right near the toilet flange at the end. I haven't done the math yet, but eyeballing indicates it should work. One of my biggest concerns was if I would be able to entirely remove the existing vent from the tub. In my eyes it looks that it is vented through the main stack, but I'm no pro.
 

Jeff H Young

In the Trades
Messages
8,954
Reaction score
2,235
Points
113
Location
92346
I forgot to mention the sizing depending on code , But Id be running 2 inch to sink and out roof or reventing at the 3 inch stack
 

Jeff H Young

In the Trades
Messages
8,954
Reaction score
2,235
Points
113
Location
92346
If it's a single lavatory, 1-1/2" is allowed by the IPC to be a horizontal wet vent carrying just 1 DFU.

Cheers, Wayne
Thought so! Id run 2 if its convieniant though at least up to the lav with a 2x2x1 1/2 santee
 