Thread: Wiring diagram for bedroom

  1. #1
    DIY Junior Member oxicottin's Avatar
    Join Date
    Mar 2008
    Location
    Ohio
    Posts
    9

    Default Wiring diagram for bedroom

    Hello, I'm in the process of adding a bedroom and a closet in my basement and am planning out how the wiring should go. I have done wiring before but just replacing and never started a whole room before so I needed some help. Ok, now how would I do this? I wanted a outlet on each wall and a ceiling light in the bedroom and one in the closet. How would the diagram go from a breaker box? would I run 12-2 to a box in the room and split room there with 12-2 for outlets and 14-2 for lights? Thanks!

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    Why would you put the lights on the same system with the outlets? If one of them trips the breaker, the room will be in darkness. AND if you put 14/2 on that same system, you don't need 12/2 for the outlets because as soon as you do that, you have restricted the breaker to 15 amps maximum.

  3. #3
    DIY Junior Member oxicottin's Avatar
    Join Date
    Mar 2008
    Location
    Ohio
    Posts
    9

    Default

    What I wanted to do was use a 20amp breaker run 12-2 from there to the receptacles and where the light switch was break off it with 14-2 for the room light and the receptacle closest to the closest do the same via-receptacle/switch/light. Can I do this or do I have to use a 20am for the receptacle and a 15amp for the 2 lights which I think its a wast of breaker.

  4. #4
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    It's not a big deal to have the lighting on with the receptacles. The whole "you'll be in darkness" thing is kind of silly IMO. There is ALWAYS ambient light from somewhere, unless the main trips of course.

    The thing is you cannot mix wire sizes and have a breaker for the larger wire. If you mix then you must size the breaker for the smaller wire. That said, there is NO reason to mix wire sizes in a circuit. Well, none that would apply here at least. You would just be wasting the #12 by using it with #14. Your idea is an old timer's premise, although it was never legal.

    Either use all #12 with a 20A breaker, or all #14 with a 15A breaker.

  5. #5
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    Your closet will also have strict clearence requirements and allowable fixture types. Incandescent fixture need to be 12" or more from storage areas and shelf edges. No exposed bulbs. Fluorescent reduces the clearence to 6" or more.

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,399

    Default

    If the bedroom won't have anything special in it, then one 15A circuit should be fine. A small TV, alarm clock, and a few lights is easily handled on a single breaker. Now, if you want to add a microwave, frig, hot rollers, and maybe use a hair dryer, you might want to run more. Some treadmills might push the load, but not normally.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7
    DIY Junior Member oxicottin's Avatar
    Join Date
    Mar 2008
    Location
    Ohio
    Posts
    9

    Default

    Thanks everyone for the info I will stick with 12-2 the whole way and a 20amp breaker.... I had another question, My GF gutted her 1 bedroom house and tore all the wiring out and wanted to rewire the way she wanted it and asked me to help. I told her I would post a drawling if she provided me with one and mabe the helpfull people of the forum would help with a drawling. Well here it is. She just had a new 200amp box installed and nothing is wired to it so she is starting from scratch. Here is a pic of what she wants to do how would the wiring go? Thanks!


  8. #8

    Default

    Before you start framing and wiring, where is your required egress from the bedroom directly to the outside?
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    Cone on! You are kidding, right? You expect us to give you a COMPLETE wiring diagram for a residence we have never seen? That is why electricans go to school and serve apprenticeships.

  10. #10
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Speedy Petey View Post
    It's not a big deal to have the lighting on with the receptacles. The whole "you'll be in darkness" thing is kind of silly IMO. There is ALWAYS ambient light from somewhere, unless the main trips of course.
    I have had more power failures than tripped breakers in my entire life. Some can come up with the silliest ideas

  11. #11
    DIY Junior Member CapstanRec's Avatar
    Join Date
    Sep 2010
    Location
    New Orleans
    Posts
    23

    Default

    Per current NEC, bedroom outlets (defined by NEC as both receptacles and lights) are required to be on Arc Fault Circuit Interupter breakers (AFCIs). These breakers are expensive and that's why many new homes combine lights and receptacles in bedrooms. It reduces the number of overall AFCIs. In my home, I made sure my lights and receptacles are never on the same circuit. There's nothing more annoying than plugging in something that draws a nice amount of current and have flickering lights. That's one reason bathroom receptacles now require a dedicated branch. Think hair dryer.

  12. #12
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,399

    Default

    There are some strict rules about how many receptacles are required based on the length of the walls. What you'll end up with is far more than a typical, older house had installed. the idea is to have an outlet in places so you don't have to run extension cords.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  13. #13
    DIY Junior Member CapstanRec's Avatar
    Join Date
    Sep 2010
    Location
    New Orleans
    Posts
    23

    Default

    A receptacle must be 6' from any point along a wall... 6' is the typical length of a cord on a lamp or other electronic device. If the receptacles are placed in this matter, an extension chord will rarely be used in the home... and the less extension cords the better.

  14. #14
    DIY Junior Member blazer45's Avatar
    Join Date
    Oct 2010
    Location
    Australia
    Posts
    10

    Default

    This thread really helpful a lot to us. And I also know now something about electrical wiring in bedroom. thanks!

  15. #15
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by blazer45 View Post
    This thread really helpful a lot to us. And I also know now something about electrical wiring in bedroom. thanks!
    The sparks in the bedroom should not come from the wiring.

    If there is no "penalty" for putting the room on two breakers I'd put it on two breakers.
    Last edited by Thatguy; 11-01-2010 at 05:38 PM.

Similar Threads

  1. Can someone double check my wiring diagram?
    By dizzo72 in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 04-11-2010, 11:14 AM
  2. Wiring Diagram for Bathroom
    By nelsonba in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 12-03-2007, 08:28 PM
  3. new floor in bedroom...ever use this stuff?
    By surfbug in forum Remodel Forum & Blog
    Replies: 3
    Last Post: 01-19-2007, 10:22 PM
  4. Addition to Bedroom ???
    By Bigbobdallas in forum Remodel Forum & Blog
    Replies: 0
    Last Post: 08-31-2006, 06:46 AM
  5. bedroom window
    By johnapril in forum Remodel Forum & Blog
    Replies: 12
    Last Post: 05-09-2006, 07:22 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •