Thread: 240v 2 pole grounding switch to receptacle

  1. #1

    Default 240v 2 pole grounding switch to receptacle

    For the convenience of winterizing and child safety reasons I need to hook a 10g 3wire with a ground (4 wires) to a (grounding 2 pole on/off switch) and from there to a (240v 2-pole 3 wire grounding receptacle) so I can plug in an irrigation pump and turn it on and off with the switch.
    Thanks Riley

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Sounds like a good idea.
    Curious. Why the 4-wire feed?
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  3. #3

    Default

    That's the wire that was available at the site. Riley

  4. #4

    Default

    Ps; so how do I hook it up, Pete? Riley

  5. #5
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Oh.

    First off, ignore the white wire in the feed. You do not need it.
    Grounding everything is assumed, including the switch.
    The two hot wires of the feed to L1 & L2 (LINE) on the switch.
    The two hots to the motor to T1 & T2 (LOAD) on the switch.

    If the switch is not marked you'll have to figure out which two screws are line and which two are load.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  6. #6

    Default

    Thanks Pete, and I'll think twice about getting an Advanta credit card.