Breaking street els

Users who are viewing this thread

tagyerit

New Member
Messages
1
Reaction score
0
Points
0
OK..I installed a system about 5 years ago and it seems that the street els going to the sprinkler body's keep breaking out. Do you think it is due to over tightening them or maybe is the brand (orbit) the problem. Im having about a 20 percent blowout rate.

Thanks
 

hj

Master Plumber
Messages
33,608
Reaction score
1,047
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
street ells

They are very intolerent of any kind of stress, the same as male adapters. If you do not have a space problem a short cut off end from a sch.80 threaded nipple screwed into the valve with an elbow glued to the other end will be countless times stronger.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
If you are talking about a street ell used to make a connection to the individual heads, then of course they see a lot of stress as the heads are walked on. The very best way to install sprinkler heads is to assemble with the Marlex elbows and a short piece of funny pipe.
 
Top