New pump system for my semi-artesian well and has been working fine until we disconnected and reinstalled the tank under new base cabinet.
After reconnecting (leaving the originally set 30-50 psi range) the tank now cuts-in at 30 psi as usual but cuts-out at around 33 psi, giving an apparent short cycle. I checked the air pressure and it is set to 28 psi (measured with the tank drained).
I figured the cut-in to cut-off range got reset some how. I adjusted the nut by tightening it by 10 turns or more and it did not change. None of the controls were tampered with during the setup and protective cover remained on the whole time.
Any suggestions, first time well and pump owner?
After reconnecting (leaving the originally set 30-50 psi range) the tank now cuts-in at 30 psi as usual but cuts-out at around 33 psi, giving an apparent short cycle. I checked the air pressure and it is set to 28 psi (measured with the tank drained).
I figured the cut-in to cut-off range got reset some how. I adjusted the nut by tightening it by 10 turns or more and it did not change. None of the controls were tampered with during the setup and protective cover remained on the whole time.
Any suggestions, first time well and pump owner?