I am going to help a friend finish out his attic. On one wall there is a vent pipe for the bathroom directly below it. Would it be lgal to tie into this vent as a drain for a sink in his new wet bar?
 

Construct30

New Member
Messages
588
Reaction score
0
Points
0
Location
NorthWest PA
IRC/IPC and most codes NO. You cannot wet vent between floors. If it were a waste stack and there were other vents for the floor below tied in above then yes.

dwv_b2.jpg
 
Last edited by a moderator:

tone100

New Member
Messages
2
Reaction score
0
Points
0
Since the vent is coming straight up from the bottom of the wall I guess this isn't going to work. The walls are finished downstairs so I have no way of knowing how its setup. Thanks for the answers.
 

Garrett

In the Trades
Messages
15
Reaction score
0
Points
0
Location
Georgia
Website
www.garrettplumbingco.com
except for your re-vent below flood rim level. also, why did you individually vent the water closet. seriously over vented but perhaps thats code in your area.
 