The 2008 code requires AFCI protection for ALL new 120 Volt circuits in residences. You should pull your permit before the 2008 applies in your jurisdiction to avoid that expensive stupidity.
Existing circuits usually don't fall under the new code.
The 2008 code requires AFCI protection for ALL new 120 Volt circuits in residences. You should pull your permit before the 2008 applies in your jurisdiction to avoid that expensive stupidity.
Existing circuits usually don't fall under the new code.
Not quite. Only 15- and 20-amp circuits, and only those suppyling "family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreational rooms, closets, hallways, or similar rooms or areas..."
Note that garages, laundry rooms, kitchens, baths, basements, crawlspaces, and exterior outlets are missing from that list.
I already have my permit. I am under the impression that my job must be in compliance with current codes on the date it is inspected, regardless of when the permit was issued.
I already have my permit. I am under the impression that my job must be in compliance with current codes on the date it is inspected, regardless of when the permit was issued.
How could that possibly be?
What if you get a rough-in on 12/27/07 and a finish inspection on 1/27/08? Are you suggesting they would use the '08 code for the final???
When (if they do) are they going to adopt the '08 in your area?.... that's the critical point you need to find out. Many places don't adopt the '08 automatically on Jan. 1, 2008. Some places may take two or three years to begin enforcing it.