I herd that arc fault requirements are going to be expanded soon.
For more information go here
Also, some AHJs are adopting the '08 and are modifying it so AFCIs are not required.
Just my 2¢ worth.
Not quite. Only 15- and 20-amp circuits, and only those suppyling "family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreational rooms, closets, hallways, or similar rooms or areas..."
Note that garages, laundry rooms, kitchens, baths, basements, crawlspaces, and exterior outlets are missing from that list.
2008 NEC 210.12(B).
Just my 2¢ worth.
Since hard wired smoke detectors and lights are in bedrooms, will they also need ARC fault protection?
When (if they do) are they going to adopt the '08 in your area?.... that's the critical point you need to find out. Many places don't adopt the '08 automatically on Jan. 1, 2008. Some places may take two or three years to begin enforcing it.
Just my 2¢ worth.