First time posting here, so please bare with me.

I am looking for advice on how to vent my upstairs bathroom that we're in the process of remodeling.

The original venting design utilized a 1.5" drain from the lav as a wet vent. (pic. original plumbing 1)

In this remodel we will be adding another sink, and by doing this I believe this wet vent would no longer be up to Michigan's plumbing code (IPC 2015), as defined in Table 911.3 the maximum discharge from upper fixture drain would be 1 dfu for the current pipe size.

https://up.codes/viewer/michigan/mi-plumbing-code-2015/chapter/9/vents#911.3

I believe this wet vent would now need to be 2" (min). Unfortunately part of this remodel also required us to move our vent over to another wall and there isn't enough clearance here to make this pipe 2".(pic moved vent 1 )

I am thinking that my best option now is to abandon the old sink drain and run a separate 2" drain from the new double sink over to the shower. In this process I would also vent up from the new double sink and tie it back into the old vent in the attic. I would take the old abandoned 1.5" drain and keep it as a dry vent for the toilet and shower. (picture old and new layout)

Any advice or suggestions on how I could improve upon this, or if it would even be acceptable would be greatly appreciated.

Thanks'

Mark
 

Attachments

  • Origanl Plumbing 1.jpg
    Origanl Plumbing 1.jpg
    100.9 KB · Views: 211
  • Old and New layout.jpg
    Old and New layout.jpg
    60.1 KB · Views: 218
  • moved vent 1.jpg
    moved vent 1.jpg
    80.8 KB · Views: 225

wwhitney

In the Trades
Messages
6,592
Reaction score
1,858
Points
113
Location
Berkeley, CA
If your previous configuration had no dry vent for the toilet or the shower, it wasn't a compliant wet vent layout. For a dry vented fixture to horizontal wet vent other fixtures, there can be at most one wet vented fixture up stream of it. But your previous configuration had the toilet and shower combining with neither fixture vented.

Your proposed drawing looks good, and you don't need that short green section in the bottom right corner. The vented double lav drain wet vents the shower and the toilet, and at the 3" stack, you just need a quarter bend to turn the toilet down, no vent take off there.

Cheers, Wayne
 

MARKJD

New Member
Messages
3
Reaction score
0
Points
1
Location
Michigan
Wayne,

First and foremost thank you for your input. It is greatly appreciated.

My house was built in the 70's and the toilet here is plumbed with cast iron. Would you recommend switching this over to PVC? I have the floors open and the access is there, but if its not necessary I would just presume to leave it in place.

Thanks,

Mark
 

wwhitney

In the Trades
Messages
6,592
Reaction score
1,858
Points
113
Location
Berkeley, CA
I don't know how to evaluate if the existing cast iron is sufficiently corroded for replacement to be prudent. For replacement, I would prefer cast iron over PVC for drains over living space.

Cheers, Wayne
 