I am in the process of planning a basement remodel. I am unsure what was/wasn't done with permits/code and looking for help on the feasibility of my project meeting code.
TL/DR: 2015 IPC, Existing 14.2 WSFU demand (plus 2 hose bibs?). Planned 17.8 (+2 hose bibs) wsfu demand. 3/4" supply into basement main valve, 3/4" main distribution branch almost the full length of just under 50ft inside the house. House is ~30ft from the street with no access holes for outside main valve in sight. 2 floors, 3br/2ba. Kitchen/laundry. Want to add a full basement bathroom. Code books seems to indicate 3/4" is too small even for existing. I will assume 50 psi water pressure until I measure it ( I think a read somewhere 50+ is standard for my area). So Questions...
#1: Did I screw up, if so on what?
#2: If this is not sufficient for existing and/or adding a bathroom, will 1" Distribution pipe cover existing and/or planned demand, realistically and according to code?
#3: Where does "Distribution pipe" start and end? I think I read it starts at the inside water main valve, I assume it ends at the ends at the furthest fixture. I am willing to up the pipe from there, but if I have to dig out to the street/front yard, I will abandon this dream, for now.
More details:
My area uses 2015 IPC. Here is what my house has:
Master bath group:
1 Shower
1 Water Closet (1.28 gpf)
1 Lavatory
Main floor bath group:
1 Bathtub/shower
1 Water Closet (1.28 gpf)
1 Lavatory
Kitchen:
Sink + Dishwasher
Laundry:
1 "Laundry Tray" (utility sink)
1 Washing Machine
Other:
1 Wet bar sink (I assume this is similar to kitchen sink, unless a Lavatory counts, for now)
**2 hose bibs (outside) Not supplying anything "constantly", not sure what value to use.
+Addition plan:
1 Basement bathroom group
Water Supply Calculations
According to table 103.3(2) I get this (wsfu) total: 14.2+ (17.8+ after adding another bathroom)
Master Bath (3.6) + Main floor bath (3.6) + Kitchen sink/DW (2.8) + Laundry washer+sink (2.8) + wet bar sink (1.4)
With adding a full bathroom group to the basement, add 3.6 for a new total of 17.8 wsfu.
According to (all pressures) Table E201.1 indicates, "3/4 inch Meter and Service Pipe" with "3/4 inch Distribution Pipe" The maximum wsfu is 9.2 for 3/4", 3/4" pipe. This seems absurdly low for 3/4" pipe. My parents house has a similar number of fixtures, MUCH more (longer) pipe (same 3/4") and supplies more than my house existing does. Their house has one less bathtub than I plan to have after the remodel. No problems in that house when it was packed with MANY people.
Using 3/4" Service pipe and 1" Distribution pipe jumps up dramatically to 32 WSFE @ 80ft length, and 18 wsfu up to 150 ft developed length (generous margin here).
Using Terry's posted tables here I have:
Existing wsfu: 27 (3/4 x 3/4 not sufficient)
Planned wsfu: 34.5 (3/4 x 1 marginally sufficient if equivalent total length is under 80ft, its close, 3/4 x 1.25 very sufficient)
TL/DR: 2015 IPC, Existing 14.2 WSFU demand (plus 2 hose bibs?). Planned 17.8 (+2 hose bibs) wsfu demand. 3/4" supply into basement main valve, 3/4" main distribution branch almost the full length of just under 50ft inside the house. House is ~30ft from the street with no access holes for outside main valve in sight. 2 floors, 3br/2ba. Kitchen/laundry. Want to add a full basement bathroom. Code books seems to indicate 3/4" is too small even for existing. I will assume 50 psi water pressure until I measure it ( I think a read somewhere 50+ is standard for my area). So Questions...
#1: Did I screw up, if so on what?
#2: If this is not sufficient for existing and/or adding a bathroom, will 1" Distribution pipe cover existing and/or planned demand, realistically and according to code?
#3: Where does "Distribution pipe" start and end? I think I read it starts at the inside water main valve, I assume it ends at the ends at the furthest fixture. I am willing to up the pipe from there, but if I have to dig out to the street/front yard, I will abandon this dream, for now.
More details:
My area uses 2015 IPC. Here is what my house has:
Master bath group:
1 Shower
1 Water Closet (1.28 gpf)
1 Lavatory
Main floor bath group:
1 Bathtub/shower
1 Water Closet (1.28 gpf)
1 Lavatory
Kitchen:
Sink + Dishwasher
Laundry:
1 "Laundry Tray" (utility sink)
1 Washing Machine
Other:
1 Wet bar sink (I assume this is similar to kitchen sink, unless a Lavatory counts, for now)
**2 hose bibs (outside) Not supplying anything "constantly", not sure what value to use.
+Addition plan:
1 Basement bathroom group
Water Supply Calculations
According to table 103.3(2) I get this (wsfu) total: 14.2+ (17.8+ after adding another bathroom)
Master Bath (3.6) + Main floor bath (3.6) + Kitchen sink/DW (2.8) + Laundry washer+sink (2.8) + wet bar sink (1.4)
With adding a full bathroom group to the basement, add 3.6 for a new total of 17.8 wsfu.
According to (all pressures) Table E201.1 indicates, "3/4 inch Meter and Service Pipe" with "3/4 inch Distribution Pipe" The maximum wsfu is 9.2 for 3/4", 3/4" pipe. This seems absurdly low for 3/4" pipe. My parents house has a similar number of fixtures, MUCH more (longer) pipe (same 3/4") and supplies more than my house existing does. Their house has one less bathtub than I plan to have after the remodel. No problems in that house when it was packed with MANY people.
Using 3/4" Service pipe and 1" Distribution pipe jumps up dramatically to 32 WSFE @ 80ft length, and 18 wsfu up to 150 ft developed length (generous margin here).
Using Terry's posted tables here I have:
Existing wsfu: 27 (3/4 x 3/4 not sufficient)
Planned wsfu: 34.5 (3/4 x 1 marginally sufficient if equivalent total length is under 80ft, its close, 3/4 x 1.25 very sufficient)