Venting Saniflo pump up system

Users who are viewing this thread

Charp

Member
Messages
41
Reaction score
1
Points
8
Location
Grass Valley, California
I will soon be installing a SanifloAccess 3 system in my daylight basement. A few years ago when remodeling the room above I had a rare moment of foresight and installed a 1 1/2" or 2" (I need to measure it) vent pipe in the wall and through the roof. My question is about venting the drain pipe from the shower to the pump tank and from the sink to the pump tank. Shower drain pipe will be less than 36" and the sink will be less than 60". Is the vent connection on the Saniflo tank sufficient for all the fixtures?

Thanks
 

Jeff H Young

In the Trades
Messages
9,081
Reaction score
2,278
Points
113
Location
92346
you might want to a little check with the AHJ as code says they must approve a macerating toilet over a sewer ejector. some of those have 1-1/2 vent and UPC requires 2" so that may or may not be an issue. As for tieing those other 2 vents don't know but if your not running up with a 2 inch I wouldn't expect a w/c, lav and shower to fly on 1-1/2 vent
 

Jeff H Young

In the Trades
Messages
9,081
Reaction score
2,278
Points
113
Location
92346
section 710.13 explains it pretty well . need approval of inspector and follow manufactures guidelines
 