Under-slab basement bath DVW scheme

Users who are viewing this thread

3D Artist

New Member
Messages
22
Reaction score
0
Points
1
Location
SW FL
Is this looking OK? No rolled wyes or tees. Everything connecting at the same level, about. Shower 2" routing around the WC 3" to drain into the 2" which is serving as the vent for the shower and the WC.
 

Attachments

  • 2020-10-12 12_14_28-DWV floor zero ensuite bath.skp - SketchUp Make 2017.png
    2020-10-12 12_14_28-DWV floor zero ensuite bath.skp - SketchUp Make 2017.png
    50.2 KB · Views: 187
  • 2020-10-12 12_16_11-Chief Architect Premier X12.png
    2020-10-12 12_16_11-Chief Architect Premier X12.png
    58.8 KB · Views: 141

wwhitney

In the Trades
Messages
6,592
Reaction score
1,858
Points
113
Location
Berkeley, CA
Looks good to me as long as the shower trap arm length is within limits. In fact the layout shown is a UPC-complaint wet vent, while Florida is under the IPC, which has less strict requirements. Under the IPC you don't need to have the toilet as the last fixture on the wet vent. The IPC also only requires a 1-1/2" vent.

Cheers, Wayne
 