Is this looking OK? No rolled wyes or tees. Everything connecting at the same level, about. Shower 2" routing around the WC 3" to drain into the 2" which is serving as the vent for the shower and the WC.
Attachments
2020-10-12 12_14_28-DWV floor zero ensuite bath.skp - SketchUp Make 2017.png
50.2 KB
· Views: 187
2020-10-12 12_16_11-Chief Architect Premier X12.png
Looks good to me as long as the shower trap arm length is within limits. In fact the layout shown is a UPC-complaint wet vent, while Florida is under the IPC, which has less strict requirements. Under the IPC you don't need to have the toilet as the last fixture on the wet vent. The IPC also only requires a 1-1/2" vent.