This layout is for a small bathroom in an apartment with a garage underneath. Is this a good plumbing design that meets code (I've attempted to do so)? Or would it be better to tie the tub drain in closer to the 3" vertical stack? Any other suggestions?

PXL_20231209_020723833.jpg
 

Marzec

New Member
Messages
23
Reaction score
2
Points
3
Location
Ohio
only need 1 1/2" dry vent
Thanks for your input. Why is a dry vent needed in addition to the wet vent? This diagram is similar to one out of the IPC except in that example there is a horizontal main line rather than a vertical stack.
 

Jeff H Young

In the Trades
Messages
8,976
Reaction score
2,242
Points
113
Location
92346
At top of your drawing where you wrote "wet vent " that section is a dry vent and can be 1 1/2 down to the san tee so the san tee would be 2x 1 1/2 x1 1/2
 

Marzec

New Member
Messages
23
Reaction score
2
Points
3
Location
Ohio
At top of your drawing where you wrote "wet vent " that section is a dry vent and can be 1 1/2 down to the san tee so the san tee would be 2x 1 1/2 x1 1/2
Now I understand what you meant. I thought you were saying I needed to add a dry vent to complete the design. But you're saying the dry vent section only needs to be 1 1/2".

I labeled it "wet vent" since it becomes a wet vent below the lav drain, but where I labeled it it's definitely dry. Thanks for pointing out that distinction. Also, there is an existing 2" galvanized steel dry vent (transitioning to 4" CI through the roof) already in place so I'll just be using a no hub fitting above the lav drain and transitioning to 2" PVC.
 

John Gayewski

In the Trades
Messages
4,366
Reaction score
1,349
Points
113
Location
Iowa
A vertical wet vent needs to be two sizes bigger than the drain served. Since your tub is 1.5" the section that vents the toilet and serves the tub should be 3"pipe. I think this is true in the ipc, I know it's true in the upc.

It's possible I'm wrong and the ipc wet vent sections are governed by fixture units. You'd have to look in the related sections to find out that sections pipe size to be sure.
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
A vertical wet vent needs to be two sizes bigger than the drain served.
It's just one pipe size larger, not two, for the UPC:


For the IPC, wet vent sizing doesn't differentiate between horizontal and vertical. And just two fixtures on a vertical wet vent is considered "common venting at different levels," rather than vertical wet venting, which is restricted to bathroom groups.


Cheers, Wayne
 

Jeff H Young

In the Trades
Messages
8,976
Reaction score
2,242
Points
113
Location
92346
Now I understand what you meant. I thought you were saying I needed to add a dry vent to complete the design. But you're saying the dry vent section only needs to be 1 1/2".

I labeled it "wet vent" since it becomes a wet vent below the lav drain, but where I labeled it it's definitely dry. Thanks for pointing out that distinction. Also, there is an existing 2" galvanized steel dry vent (transitioning to 4" CI through the roof) already in place so I'll just be using a no hub fitting above the lav drain and transitioning to 2" PVC.
Great its all good ! just use the proper band if its being inspected, here is a little tip, run your pvc above the sink top around 6 inches for your plastic to gal connection because water will never be there and it will never be cause of a leak
 

John Gayewski

In the Trades
Messages
4,366
Reaction score
1,349
Points
113
Location
Iowa
It's just one pipe size larger, not two, for the UPC:


Sorry yes. But this section would still needs to be 3" under upc. As there's more than one fixture draining into the vertical wet vent we would need to be one pipe size larger than the combined dfu minimum. Minimum pipe size for 3 dfu's would be 2". We then go up to 3".

IPC is outta my range slowly learning it.
 