Need to replace move drain stack between first floor and second floor. Current cast iron stack is probably about 70 years old. Can't save the stack most likely and I want to keep the sound transmission low. Could I use 4" schedule 80 pipe instead of replacing with no hub cast iron?
 

John Gayewski

In the Trades
Messages
4,426
Reaction score
1,383
Points
113
Location
Iowa
Need to replace move drain stack between first floor and second floor. Current cast iron stack is probably about 70 years old. Can't save the stack most likely and I want to keep the sound transmission low. Could I use 4" schedule 80 pipe instead of replacing with no hub cast iron?
No. I hope your talking about plastic. But the ID of sched 80 will be smaller than what you have in place now. If for some reason the ID is the same (cast iron can have some odd dimensions) then you could, but why not just keep the material consistent?
 

Reach4

Well-Known Member
Messages
38,964
Reaction score
4,463
Points
113
Location
IL
Schedule 80 might be even better than solid schedule 40 PVC. That was not included in the testing in this video:
 

GrumpyPlumber

Licensed Grump
Messages
1,521
Reaction score
57
Points
48
Location
Licensed Grump
Sched 80 also won't be soundproof. In my state we cannot place PVC between cast iron on the vertical for the fact that PVC swells 3/8" per 10' when heated 100 degrees and can gradually loosen old lead/oakum joints.
 