Hi everyone, need your thoughts regarding increase in pressure in my hydronic system as of lately, setting off my 30# release valve.
Boiler specs:
McClain early 90s natural gas, ~50gallon cast iron boiler, connected to cast iron baseboards in 1800 SQF house.
boiler water temps set to 190 and 170. (using a infrared thermometer, i can confirm that the water immediately exiting the boilers never gets over 195 and the temp gauge on the boiler itself never goes over 190 either)
Issue: periodically the pressure in the system climbs to 31PSI , which triggers the 30# pressure release valve.
Issue started last year. Which was solved (so i thought) by replacing the previously installed expansion tank with an extrol Ex-30 (
Prior to that i replaced the water feed line valve which was set from factory at 15pounds.)
After that, there was no issue in 2021.
This winter, the same symptoms occur. once in a while, ( seems like its only in the mornings when house recovers from overnight setback) that the pressure builds to 31# setting off the release valve.
Once the house is back up to daytime temps, the pressure on the boiler stays at a steady 25-28#.
at the install of the expansion tank , i initially pressurized it to the incoming water pressure. 15#.
i can confirm that the water pressure regulator is working properly because when the boiler cools down, pressure drops to 15 pounds. So i know the valve is working properly. ( i have also shut off the inlet water feed to test just in case)
Obviously since the pressure is going above 15# when the heat runs, the expansion tank is getting water logged.
So i increased pressure in the expansion tank each day to see if it would solve my issues. Currently im up to 25# in the expansion tank. Which, is pointless since the boiler pressure is getting to 31. So its still getting water logged.
These are my thoughts, and please let me know what you think.
Even though the system has been fine for years with the current set up ( at least so i think) , i was debating on removing the ex-30 expansion tank, and replacing it with a Ex-60 or larger. And setting the expansion tank pressure to 20-25 pounds?
My thought is that a larger expansion tank will provide more room for expansion and the pressure wont raise up to the 30#?
Why this started happening last year is beyond me. the only thing i can assume is:
1- the original ex30 is was not the appropriate size to begin.
2- 190 is too high for the hi-temp setting? even though water temp at pipe exit doesnt get over 195
3- rust build up in the boiler making the ~50 gallon tank a smaller boiler, but that shouldn't matter i dont think, that means the flame would just cycle on and off more.
4- a defective new ex-30? i CAN feel the temp on the expansion tank change as the pressure increases. and cool down when the system drops back to 15# so it SEEMS like it is working. (infra red thermometer confirms change in temp on ex tank) however, being set to 20# and the system hitting 30# then obviously its water logged after 20.
I also ensured the ex-30 and the lines were properly bled and there is no air trapped in the system.
here are some pics because its always nice to see pictures.
thanks!
Boiler specs:
McClain early 90s natural gas, ~50gallon cast iron boiler, connected to cast iron baseboards in 1800 SQF house.
boiler water temps set to 190 and 170. (using a infrared thermometer, i can confirm that the water immediately exiting the boilers never gets over 195 and the temp gauge on the boiler itself never goes over 190 either)
Issue: periodically the pressure in the system climbs to 31PSI , which triggers the 30# pressure release valve.
Issue started last year. Which was solved (so i thought) by replacing the previously installed expansion tank with an extrol Ex-30 (
Prior to that i replaced the water feed line valve which was set from factory at 15pounds.)
After that, there was no issue in 2021.
This winter, the same symptoms occur. once in a while, ( seems like its only in the mornings when house recovers from overnight setback) that the pressure builds to 31# setting off the release valve.
Once the house is back up to daytime temps, the pressure on the boiler stays at a steady 25-28#.
at the install of the expansion tank , i initially pressurized it to the incoming water pressure. 15#.
i can confirm that the water pressure regulator is working properly because when the boiler cools down, pressure drops to 15 pounds. So i know the valve is working properly. ( i have also shut off the inlet water feed to test just in case)
Obviously since the pressure is going above 15# when the heat runs, the expansion tank is getting water logged.
So i increased pressure in the expansion tank each day to see if it would solve my issues. Currently im up to 25# in the expansion tank. Which, is pointless since the boiler pressure is getting to 31. So its still getting water logged.
These are my thoughts, and please let me know what you think.
Even though the system has been fine for years with the current set up ( at least so i think) , i was debating on removing the ex-30 expansion tank, and replacing it with a Ex-60 or larger. And setting the expansion tank pressure to 20-25 pounds?
My thought is that a larger expansion tank will provide more room for expansion and the pressure wont raise up to the 30#?
Why this started happening last year is beyond me. the only thing i can assume is:
1- the original ex30 is was not the appropriate size to begin.
2- 190 is too high for the hi-temp setting? even though water temp at pipe exit doesnt get over 195
3- rust build up in the boiler making the ~50 gallon tank a smaller boiler, but that shouldn't matter i dont think, that means the flame would just cycle on and off more.
4- a defective new ex-30? i CAN feel the temp on the expansion tank change as the pressure increases. and cool down when the system drops back to 15# so it SEEMS like it is working. (infra red thermometer confirms change in temp on ex tank) however, being set to 20# and the system hitting 30# then obviously its water logged after 20.
I also ensured the ex-30 and the lines were properly bled and there is no air trapped in the system.
here are some pics because its always nice to see pictures.
thanks!