pressure tank

Users who are viewing this thread

djones68

New Member
Messages
1
Reaction score
0
Points
1
Location
mississippi
i have a 40 gal electric hot water tank and have 80 psi at the out side faucet. went and got a 2 gal presure tank with 40 pi already in it with max 80 psi will this work or do i need and bigger tank or can add more air and be ok
 
Last edited:

WorthFlorida

Clinical Trail 5th session completed 4/24/24.
Messages
5,763
Solutions
1
Reaction score
998
Points
113
Location
Orlando, Florida
i have a 40 gal electric hot water tank and have 80 psi at the out side faucet. went and got a 2 gal presure tank with 40 pi already in it with max 80 psi will this work or do i need and bigger tank or can add more air and be ok
As LLigetfa suggest, if your water pressure during the day is 80 psi, the expansion tank needs to be pre charged at 80 psi. It's an expansion tank, not a pressure tank.

A 2 gallon is just right for a 40 gallon tank. A 40 gallon will expand about 1/2 gallon.
 