Jeff H Young
In the Trades
FWIW, my utility use Badger Recordall meters, and from their published data, at 20 gpm their meters will drop:
Model 25 5/8" 6 psi
Model 25 5/8" x 3/4" 4.6 psi
Model 35 3/4" 3.3 psi
Model 55 1" 1 psi
Model 70 1" 1 psi
Cheers, Wayne
I notice that the tables Terry has doesn't show 5/8 meters or even 3/4 with larger than 1 1/2" water service . sizing method for a particular code might not consider a 2 inch to carry more fixture units than a 1 1/2" . My code books are very old and haven't sized anything like this in a very long time. I have however had many jobs with meters that are probably undersized. they by no means generally need to be equal in size to to the house line