Kitchen Waste pipe tied into existing Laundry room waste line , sizing concern.

Users who are viewing this thread

Slinkbuffalo

New Member
Messages
1
Reaction score
0
Points
1
Location
North Carolina
Hi All, I’m in the process of completing a kitchen remodel in a 100 year old house. My question is, would it be okay to tie a new 2 inch PVC waste line from the kitchen with a dishwasher to an existing 2 inch PVC pipe currently used only by the clothes washer? The Clothes washer is upstream. My concern is that the pipe is too small to handle a kitchen and laundry room at the same time. Thoughts? Thanks in advance!
 

Breplum

Licensed plumbing contractor
Messages
1,966
Reaction score
798
Points
113
Location
San Francisco Bay Area
2" is fine. The allowed load for a two inch drain pipe in horizontal layout would allow two clothes washers AND Kitchen sink with DW. 2" Vertical can handle even way more.
 