I have a Amana single split AC 3 ton. For some reason the FAN ONLY function does not work, everything else work fine. I did the following test:
I removed the T-stat cover. jumped R,G,Y 3 wires, condenser started, furnace blower also started. If I only jump R and G, the blower will not work , condenser will not work either. I remember I jumped R and G before, the blower started right away, but now, the blower does not work anymore. What can cause this problem ? Thanks.
 

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
This must be checked and diagnosed by a tech, to eliminate any guessing that can lead to unnecessary and expensive part replacements. Money worth spending right now before summer heat. If you wait one month, you won't be able to find a tech.

Usually, dead blower could mean: power supply to the blower problem OR transformer problem OR Tstat OR just burnt blower motor.
 

clocert

New Member
Messages
14
Reaction score
0
Points
1
Location
Texas
Thanks, I believe I found the problem. Checked control board, the green wire was lose at the terminal. re-attach the wire. everything OK now.
 