Retired Defense Industry Engineer xxx
Code calls for domestic water supply systems to be adjusted to NGT 80-psi...so, if yours actually does regularly get to 100, you need a PRV and an expansion tank.
Code calls for domestic water supply systems to be adjusted to NGT 80-psi...so, if yours actually does regularly get to 100, you need a PRV and an expansion tank.
How about an expansion tank aprooved for this work , installed by a qualified sprinkler fitter as per fire department regulations ?Pressure is exerted equally in every direction so whether the expansion tank is located at the far end of the line, the middle or the beginning, the tank will absorb the volume of expansion occurring in that line. If there are no back-flow devices, pressure regulators or closed isolation valves between risers or branch runs, then a single tank plumbed into one riser can absorb water expansion from all risers and branch lines.
The water within a fire suppression system will not be considered potable as it will not be flushed and replaced on a regular basis but will remain unused for long periods of time and so will become stagnate. As such, the entire fire suppression system will in effect become a dead end. Since it appears no chemicals or additives will be added, a regular expansion tank may be utilized but a clearly labeled or specially colored tank should ensure there is no confusion of the intended purpose for that tank or the pipe feeding it. (Think of a future owner that may want to run water to a refrigerator ice maker)
As you said the expansion tank is to be located in your basement, I anticipate the fire suppression system water also enters through the basement. As such, it would then seem the expansion tank will be Tee'd into the beginning of a riser, not at a dead-end of a riser or horizontal branch line. The line feeding the expansion tank may not be considered a dead-end branch as some amount of water will pass through that line in either direction while the water within the fire suppression system either expands or contracts.
Pressure is exerted equally in every direction so whether the expansion tank is located at the far end of the line, the middle or the beginning, the tank will absorb the volume of expansion occurring in that line. If there are no back-flow devices, pressure regulators or closed isolation valves between risers or branch runs, then a single tank plumbed into one riser can absorb water expansion from all risers and branch lines.
Bannerman said:...specially colored tank should ensure there is no confusion of the intended purpose for that tank or the pipe feeding it.
Bannerman said:The line feeding the expansion tank may not be considered a dead-end branch as some amount of water will pass through that line in either direction while the water within the fire suppression system either expands or contracts.
If you precharge the ET properly, under normal system pressure before expansion, there's very little water stored in the tank, so the majority of it is expelled as soon as some is used.