Hi,
I'm wiring four new electric baseboards in my basement.
All four are 220Volt units: 500W, 500W, 1000W, 1500W, for a total of 3500W. The longest run is less than 100ft.
If I understood the NEC, putting all of this on one circuit will require a 20Amp breaker (1.25*3500W/220V), and the wire can be #12AWG.
Did I get that right, and am I missing any other design factor?
Many thanks
Theodore