Again, forget the first hour delivery- this is a first 15 minutes time.
Again, a 127MBH AHRI net-water boiler is ABSOLUTELY GROTEQUELY oversized for your house, unless you sleep with all the windows open or the house is more than 12,000 square feet.
Oversizing a space heating boiler that badly has a fairly significant (negative) impact on the as-used efficiency. DON'T DO IT! You probably don't even have enough radiation in the whole house to even emit that much heat at an entering water temp of 180F, which means it will be prone to short cycling into even lower efficiency. (Do you have 300 feet of 8-10" tall fin-tube baseboard, or equivalent?)
A typical 2500' house in Seattle has design heat load less than 30,000 BTU/hr (30MBH) , and a better tighter house that size can have a heat load under 20,000 BTU/hr (20 MBH). If you have a heating history on this place, run this napkin-math to get a handle on your actual heat load. Total up the amount of radiation in the house, zone by zone if multi-zoned.
If you're willing to share information on zone-by-zone radiation, exact meter reading dates & amounts, and a ZIP code (for more accurate weather data) it's possible to sketch out what boiler capacity might make sense here. Don't rule out modulating condensing boilers, which can be cheaper to install and easier to get a reasonable fit to both the radiation & heat load than Godzilla-sized cast iron.
Forget the recovery rate too- with a boiler right sized for the space heating load it's too slow to make a significant difference for the first 15 minute hot water capacity numbers.
The existing storage temp is about 140F, and the total volume is 75 gallons. Simply boosting the storage temp to 160F adds only about a minute to the showering time. (See response #11). If you're not installing drainwater heat recovery it's going to need the 115.
A $1000 up-charge is better spent on drainwater heat recovery, since it will increase the apparent capacity to more than that of the 115 gallon tank, has at least 3x the service life, uses half the amount of gas for showering, and won't increase the standby loss.
I didnt see this post until after my post below was written and posted.
The person who assessed my house for the boiler size, even before we started talking at all about the indirect water tank option, recommended the US Boiler Burnham Series 3 Cast iron boiler Model 306...Input 175 MBH, Heating Capacity 146 MBH, Net AHRI rating Water 127 MBH, AFUE% 84.
My 1910 house, completely renovated in 1987, is under 3800 sq ft...with just over 1250 sq. ft. on each of 3 floors.
Our oil burning boiler is serving 7 zones plus 2 bathrooms that have radiant water heat beneath the floors.
The windows on the weather size of the house are all new double pane, and the house is well insulated.
The windows on the other side of the house are mostly single pane leaded glass.
We have a total of 22-25 cast iron radiators (without taking off all the radiator covers, I can't tell if some of them are very large or doubles, hence the number of at least 22 and maybe 25...these are the old fashioned, refurbished heavy radiators).
I was trusting his recommendation, as I was referred to his firm because of his long (32 year) experience with boilers, of which several people in Seattle simply don't work with boilers.
You are saying that the gas boiler he has recommended is vastly oversized?