Washer drain requirements

Users who are viewing this thread

Mosher

New Member
Messages
12
Reaction score
0
Points
1
Location
Ohio
hi am i allowed to run washer drain 2 in dia on the horizontal and if yes for how long
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,436
Points
113
Location
IL
after the vent
You can go a long way as long as you slope 1/4 inch per foot. There may be some limit, but if there is, I expect that limit might be over 40 ft. There is some limit as to how much turning you can do without a cleanout.
 

Mosher

New Member
Messages
12
Reaction score
0
Points
1
Location
Ohio
so whats all this talk about new washers spitting out water at a very fast rate that they require a 3 inch line
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,436
Points
113
Location
IL
so whats all this talk about new washers spitting out water at a very fast rate that they require a 3 inch line
That talk is about newer IPC wanting 3 inch after the washer drainage has joined something else. 2 inch is good if you are just carrying the washer standpipe drainage.
 