Voltage on ground

Users who are viewing this thread

Thinkly

Member
Messages
51
Reaction score
2
Points
8
Location
Kansas
I am replacing some outlets in the kitchen. I tested the ground with my voltage tester and it is indicating voltage. What could cause this?
 

Afjes

Member
Messages
98
Reaction score
37
Points
18
Location
Northeast PA
As I replied on another forum you posted on the pen tester can give you false readings. It can pick up from a hot wire elsewhere in the box which it is more than likely doing of the hot wire.

If you don't have an actual meter yet on hand purchase one. Preferrably an anologue meter with a dial and not digital. If you already have a digital that would be useful.

More than likely that ground is not hot.
 

Reach4

Well-Known Member
Messages
38,880
Reaction score
4,433
Points
113
Location
IL
Some digital multimeters have a "low impedance"/LoZ mode that can let you avoid this problem. Fluke 117 and Klein MM700 are instances, but there are certainly others. https://www.homedepot.com/p/Klein-Tools-True-RMS-Auto-Ranging-Digital-Multimeter-MM700/206517339
 
Last edited:

WorthFlorida

Clinical Trail on a Cancer Drug Started 1/31/24. ☹
Messages
5,760
Solutions
1
Reaction score
997
Points
113
Location
Orlando, Florida
Another way to pick up voltage is a shared neutral. Two circuits are sharing the neutral(white) when a 12-3 with ground is used. Kitchen counter requires two 20 amp circuit and 12-3 is used most of the time. If you turn off one, the neutral is still carrying current for the other live circuit. Voltage sensor pens may detect this.
 

LLigetfa

DIYer, not in the trades
Messages
7,507
Reaction score
581
Points
113
Location
NW Ontario, Canada
Another way to pick up voltage is a shared neutral. Two circuits are sharing the neutral(white) when a 12-3 with ground is used. Kitchen counter requires two 20 amp circuit and 12-3 is used most of the time. If you turn off one, the neutral is still carrying current for the other live circuit. Voltage sensor pens may detect this.
In the OP's video, the voltage is being detected on the protection ground, not on the neutral. The protection ground should not be carrying any current in the absence of any fault.
 