Sorry if this was covered in another post, but I wasn't able to find what I need.
Problem - valve does not open when instructed to by the controller.
Equipment
Rain bird valve/solenoid
Installed around 2017
Things I've done
1) Manually rotating the solenoid counter-clockwise will open the valve correctly.
2) Opening the breather will open the valve correctly.
3) Connecting 3 9-volt batteries in series directly to the solenoid wires (not wired to the system) will open the valve correctly.
4) Measure the voltage at the control box shows 24-ish volts.
5) Measuring the voltage at the common and trigger wire at the valve shows 24-ish volts.
6) Measuring the voltage at the common and trigger wires with the solenoid connected shows 24-ish and then drop down.
7) Two new solenoids do the same thing.
I figure it has to be a wiring issue of some kind, but that's the mystery part. Can anyone suggest some more options or things to try?
Problem - valve does not open when instructed to by the controller.
Equipment
Rain bird valve/solenoid
Installed around 2017
Things I've done
1) Manually rotating the solenoid counter-clockwise will open the valve correctly.
2) Opening the breather will open the valve correctly.
3) Connecting 3 9-volt batteries in series directly to the solenoid wires (not wired to the system) will open the valve correctly.
4) Measure the voltage at the control box shows 24-ish volts.
5) Measuring the voltage at the common and trigger wire at the valve shows 24-ish volts.
6) Measuring the voltage at the common and trigger wires with the solenoid connected shows 24-ish and then drop down.
7) Two new solenoids do the same thing.
I figure it has to be a wiring issue of some kind, but that's the mystery part. Can anyone suggest some more options or things to try?