One of our kids jacked with our Nest thermostat so much that it stopped recognizing power from the Common wire. I think it caused a fault in the actual thermostat. Regardless, I replaced the nest with a basic non-programmable Honeywell. Heat is running fine but when I switch the fan from auto to “on” nothing happens. I have attached my current wiring setup. Any suggestions? I like running the fan to even the temperature in the home, add some air movement, and some air filtration.
 

Attachments

  • IMG_9046.jpeg
    IMG_9046.jpeg
    57.6 KB · Views: 57
  • IMG_9045.jpeg
    IMG_9045.jpeg
    159 KB · Views: 49
One of our kids jacked with our Nest thermostat so much that it stopped recognizing power from the Common wire. I think it caused a fault in the actual thermostat. Regardless, I replaced the nest with a basic non-programmable Honeywell. Heat is running fine but when I switch the fan from auto to “on” nothing happens. I have attached my current wiring setup. Any suggestions? I like running the fan to even the temperature in the home, add some air movement, and some air filtration.
Jump R to G fan at stat should run . If not either G wire isn't G in furnace or wire is broken. White wire on "not used" is that common? At furnace with blower door switch taped depressed
R to W,G, Y if calling 0 vac
If not 24vac
C to W,G,Y if calling 24vac. Brand and complete model # of stat? If blower runs jumped the thermostat programing is wrong. Have to set up type of equipment.
 