Remove equipment or repurpose?

Softener_rookie

New Member
Messages
4
Reaction score
1
Points
3
Location
Oregon
My well water treatment is 25um 20" big blue bag filter, 1354 tank with 2cuft of turbidex, water softener with Crystal-Right CR-100, 1um 1 Micron 20 Inch big blue Spun Wound Polypropylene filter, and finally UV (was Hg lamp, now LED).

Water testing shows Iron and Manganese not detected after water treatment, but I am still seeing Iron and/or Manganese residue on the UV Quartz sleeve and PEX plumbing.

Back in 2016, I was originally told that I had a total of 4.1ppm of Iron (ferric + ferrous), but from experience about 50% of that was ferric. Fast forward to 2025, I got the water test lab to test ferric and ferrous Iron separately so I could determine if I really needed 2cuft of turbidex to filter out the ferric Iron. It turns out, my Iron content is way down to 0.3ppm ferrous and ferric not detectable at 0.1ppm.

I have no smells or iron bacteria. There is a residue on the inside of the toilet tank that looks like manganese, but I am not completely sure.

Question:

1)What does a guy do to get rid of Iron and/or Manganese residue that is below lab detectable limits of 0.1ppm?

2) Should I repurpose the 1354 tank with turbidex for ferric iron to something else or just leave it idle?

Thanks

UnitsMethod Reporting Limit (MRL)Untreated after well drilledUntreated after 9 yearsTreated after 3 yearsTreated after 9 Years
Date5/31/20168/8/202512/26/20198/8/2025
Treated?NoNoYesYes
pH7.557.117.757.8
Specific Conductanceumhos/cm1176.4202173.7246
Arsenicmg/l0.0020.00350.00340.0032ND
Chloridemg/l0.34.554.572.636.61
Coppermg/l0.1NDNDNDND
Fluoridemg/l0.20.291ND0.234ND
Hardness as CaCO3mg/l CaCO3107284NDND
Iron, Totalmg/l0.14.110.29NDND
Ferric Ironmg/l0.1NDND
Ferrous Ironmg/l0.10.29ND
Leadmg/l0.001NDNDNDND
Manganesemg/l0.050.210.192NDND
Nitrogen, Nitratemg/l N0.2NDNDNDND
Sodiummg/l17.527.3943.857.7
Sulfatemg/l0.28.177.013.2811.2
Zincmg/l0.1NDNDNDND
 

TJanak

Member
Messages
256
Reaction score
9
Points
18
Location
South TX
I don't have a good answer for you other than the lab's Method Reporting Limits seem marginal. 0.05 ppm for manganese isn't going to cut it, that's the generally accepted staining level for manganese, and I see staining below that.

Softener sized correctly for flow rates?
 

Softener_rookie

New Member
Messages
4
Reaction score
1
Points
3
Location
Oregon
Thanks for your feedback on manganese reporting limits. The toilet tank residue is a very light film. As an experiment, I put some Red-b-Gone in the toilet tank for 30 minutes and the tank now looks like new.

We have a two person household and we don't use alot of softened water. We use a max of 3 gpm (~80 gal per day) and the softener is sized for at least 6 gpm.

In my original message, I neglected to say that I have and 50 gpd RO drinking water system with a 40 gallon FlexRO diaphram accumulator tank. There is no solenoid shutoff on the inlet to the RO water system. I think this is a major contributor to the problem.

My VFD well pump system has a 4 gallon diaphram accumulator on the source side; no accumulator on the softened water side. Lets say my RO accumulator needs to be refilled just as my water softener goes into regen. Untreated watrer is bypassed at the softener (in regen) and fills the plumbing from my softener to my RO system. The softener is in my pole barn, goes through 50 ft of 1.25 PEX to my house, then to the RO system. All that plumbing would be filled with untreated water.

I'm planning to install a timer and solenoid shutoff on the RO water inlet. I'm also planning to replace the turbidex with katalox light unless there is a good argument not to do it.
 

TJanak

Member
Messages
256
Reaction score
9
Points
18
Location
South TX
Thanks for your feedback on manganese reporting limits. The toilet tank residue is a very light film. As an experiment, I put some Red-b-Gone in the toilet tank for 30 minutes and the tank now looks like new.

We have a two person household and we don't use alot of softened water. We use a max of 3 gpm (~80 gal per day) and the softener is sized for at least 6 gpm.

In my original message, I neglected to say that I have and 50 gpd RO drinking water system with a 40 gallon FlexRO diaphram accumulator tank. There is no solenoid shutoff on the inlet to the RO water system. I think this is a major contributor to the problem.

My VFD well pump system has a 4 gallon diaphram accumulator on the source side; no accumulator on the softened water side. Lets say my RO accumulator needs to be refilled just as my water softener goes into regen. Untreated watrer is bypassed at the softener (in regen) and fills the plumbing from my softener to my RO system. The softener is in my pole barn, goes through 50 ft of 1.25 PEX to my house, then to the RO system. All that plumbing would be filled with untreated water.

I'm planning to install a timer and solenoid shutoff on the RO water inlet. I'm also planning to replace the turbidex with katalox light unless there is a good argument not to do it.
Wow, 40 gallon RO tank. Household must use a lot of RO water.

I guess that's possible, but the timing would have to be just right, because a 50 GPD RO system uses so little water (low flow rate) that it would have to be running during the entire softener regen to draw any sort of significant amount of untreated water through the softener. And even then, I don't know if the RO could use 50' x 1-1/4" worth of water during softener regen. I guess I'm skeptical. No harm in trying the RO shutoff timer though.

I can't be helpful on the Katalox light, never used it.
 

Softener_rookie

New Member
Messages
4
Reaction score
1
Points
3
Location
Oregon
It's a 40 gallon diaphram tank; spec says it holds 30 gallons. Many times I've seen the RO system run all night. 50 feet of 1.25 pex is about 3 gallons with RO waste water using at least another 3. I agree the timing of RO system running all night during softener regen might be a stretch, but I'll eliminate this variable by putting a shutoff solenoid.

In the meantime, as an experiment, I installed an ultra filter instead of my 1 micron spun Wound Polypropylene filter right before my UV system and have captured all sorts of iron and/or manganese colloids. I believe the colloids are the problem.
 

TheH2OGuy

New Member
Messages
2
Reaction score
0
Points
1
Location
48442
My well water treatment is 25um 20" big blue bag filter, 1354 tank with 2cuft of turbidex, water softener with Crystal-Right CR-100, 1um 1 Micron 20 Inch big blue Spun Wound Polypropylene filter, and finally UV (was Hg lamp, now LED).

Water testing shows Iron and Manganese not detected after water treatment, but I am still seeing Iron and/or Manganese residue on the UV Quartz sleeve and PEX plumbing.

Back in 2016, I was originally told that I had a total of 4.1ppm of Iron (ferric + ferrous), but from experience about 50% of that was ferric. Fast forward to 2025, I got the water test lab to test ferric and ferrous Iron separately so I could determine if I really needed 2cuft of turbidex to filter out the ferric Iron. It turns out, my Iron content is way down to 0.3ppm ferrous and ferric not detectable at 0.1ppm.

I have no smells or iron bacteria. There is a residue on the inside of the toilet tank that looks like manganese, but I am not completely sure.

Question:

1)What does a guy do to get rid of Iron and/or Manganese residue that is below lab detectable limits of 0.1ppm?

2) Should I repurpose the 1354 tank with turbidex for ferric iron to something else or just leave it idle?

Thanks

UnitsMethod Reporting Limit (MRL)Untreated after well drilledUntreated after 9 yearsTreated after 3 yearsTreated after 9 Years
Date5/31/20168/8/202512/26/20198/8/2025
Treated?NoNoYesYes
pH7.557.117.757.8
Specific Conductanceumhos/cm1176.4202173.7246
Arsenicmg/l0.0020.00350.00340.0032ND
Chloridemg/l0.34.554.572.636.61
Coppermg/l0.1NDNDNDND
Fluoridemg/l0.20.291ND0.234ND
Hardness as CaCO3mg/l CaCO3107284NDND
Iron, Totalmg/l0.14.110.29NDND
Ferric Ironmg/l0.1NDND
Ferrous Ironmg/l0.10.29ND
Leadmg/l0.001NDNDNDND
Manganesemg/l0.050.210.192NDND
Nitrogen, Nitratemg/l N0.2NDNDNDND
Sodiummg/l17.527.3943.857.7
Sulfatemg/l0.28.177.013.2811.2
Zincmg/l0.1NDNDNDND
If the media in the filtration system is 9 years old, it's time for a rebed of the system. Filtration media typically last 3-5 years before it becomes too fouled to remain effective. This would account for the bleed-through of iron of 0.3ppm.
 

Softener_rookie

New Member
Messages
4
Reaction score
1
Points
3
Location
Oregon
In the 14 weeks since my original post, my water softener has regened 5 times at exactly the same time my RO water filter unit was running. Let's approximate that to "33% of the time, my water softener regens at the same time as my RO water unit is generating water". As an experiment, I replaced my 1um spun filter with a hollow fiber ultra filter. Iron residue problems are gone. The issue seems to be iron colloids.
 