Proper way to run shower trap to toilet and shower vent?

Pisti

New Member
Messages
24
Reaction score
1
Points
3
Location
Denver
I am replacing the 1 1/2" old tub drain with a 2" shower drain. My plan is to drop the drain on the near side of joists and it will enter the p-trap. I would plan on putting a sanitary tee rotated at a 45 degree angle (notched at the bottom of the joist) so I can maintain vertical rise below the flood-level rim. I would bring the pipe back towards the wall and then a 45 to bring it vertical before connecting to the current vertical vent a few feet up.

Does this seem appropriate in my scenario?


Screenshot 2026-07-20 at 9.27.08 PM.png
 
Last edited:
I am replacing the 1 1/2" old tub drain with a 2" shower drain. My plan is to drop the drain on the near side of joists and it will enter the p-trap. I would plan on putting a sanitary tee rotated at a 45 degree angle (notched at the bottom of the joist) so I can maintain vertical rise below the flood-level rim. I would bring the pipe back towards the wall and then a 45 to bring it vertical before connecting to the current vertical vent a few feet up.

Does this seem appropriate in my scenario?


View attachment 107783
I'd mainly verify the trap arm length before gluing everything together. Once you add the 45s, the developed length can be longer than it looks. Keep a consistent 1/4" per foot slope and make sure the vent ties in within the allowable trap arm distance for your local code. Also, if that sanitary tee is receiving horizontal flow, I'd use a combo or wye instead sanitary tees are generally intended for vertical flow.
 
Ok so in terms of the vent running off of the horizontal branch, a wye would be correct. It can be rotated at a 45degree to angle "vertically" back towards the wall before running up the wall? It wouldn't be laying on its side since the vent can't be horizontal below the floor-level rim. Am I understanding this right?
 
Ok so in terms of the vent running off of the horizontal branch, a wye would be correct. It can be rotated at a 45degree to angle "vertically" back towards the wall before running up the wall? It wouldn't be laying on its side since the vent can't be horizontal below the floor-level rim. Am I understanding this right?
In terms of taking a dry vent off a horizontal trap arm/fixture drain that remains horizontal, for the IPC your original proposal was fine (although I'd try to find a solution that doesn't involve notching any joists).

You could also use a wye rolled 45 degrees above horizontal/below "upright"; that actually is only pitched 30 degrees above horizontal (you'd need a 60 degree bend to turn up to vertical), so it isn't "vertical" (defined as 45 degrees or more above horizontal) but seems to be commonly accepted in this situation.

Cheers, Wayne
 
In terms of taking a dry vent off a horizontal trap arm/fixture drain that remains horizontal, for the IPC your original proposal was fine (although I'd try to find a solution that doesn't involve notching any joists).

You could also use a wye rolled 45 degrees above horizontal/below "upright"; that actually is only pitched 30 degrees above horizontal (you'd need a 60 degree bend to turn up to vertical), so it isn't "vertical" (defined as 45 degrees or more above horizontal) but seems to be commonly accepted in this situation.

Cheers, Wayne
Well unfortunately the notch that was already in place and is maxed out, doesn't give enough clearance for me to roll a fitting to 45 degrees. I am converting the bath to a shower and was wanting a vertical drop vs a horizontal stretch before the drop to the strap which is what they had. The vent also needed to move back into the wall cavity since it can't just sit under a tub any longer. Any other thoughts or suggestions?
 
It looks like the horizontal drain line is being run at an elevation so its top is just below the bottom of the joists? Assuming that can't be changed because of the elevation of the existing branch drain, can you jog the trap arm towards/under the joist, so that the fitting can roll up without hitting the joist?

Or if you are doing a center drain in your shower, maybe switch to a linear drain against one edge, for a more favorable drain location as far as trap arm routing? I.e. route the trap arm to the joist bay along the wall, then if necessary back to the adjacent joist bay to connect to the existing.

If those don't work, a current photo with the existing work removed and no mark ups would be helpful.

Cheers, Wayne
 
P.S. How do the other fixtures in the bathroom connect in? If, for example, the shower drain connects to the lav drain (within 2" of fall from the 2" shower trap), and then the combined drain connects to the WC, a single dry vent on the lav will wet vent the shower and WC, so you don't need a dry vent on the shower.

Cheers, Wayne
 
The sink is totally separate. This was a 1949 converted bedroom to bathroom in 2000. The original tub drained on the opposite side of the joist and connects into the horizontal branch which picks up the toilet and then drops down the stack. Where the tub drain connected into the horizontal run, they had the vent branching off left, and then back up through the roof.

Original plumbing pic

Screenshot 2026-07-21 at 5.46.25 PM.png



Looking back at the wye I was trying to play with and beyond that is the toilet. It runs just above the bottom of the joist here.

IMG_1054 copy Small.jpeg


Here is a view of the current situation. I was hoping to run 2" pipe for the shower drain but a trap is too tall of the ceiling below and the height of the current drain line.

asdasa.jpeg



Lastly, here is a view of the over all scene when I was dry fitting the pan. We are planning on centering the toilet on the wall as well. I have done basic plumbing work and usually feel comfortable with this type of stuff, but I have never moved a toilet. I hopefully can find a reasonably priced plumber to do that work for me and really would like to save money to do this work on my own. Thanks for taking a look.

IMG_1057 Large.jpeg
 

Attachments

  • IMG_1056 copy Small.jpeg
    IMG_1056 copy Small.jpeg
    35.7 KB · Views: 0
Are you going to have or willing to have at least a small wing wall between the shower and WC? As long as it extends from the wall past the first joist by at least 6" finished, and is at least 12" finished taller than the shower threshold, if you can't get a vent through that joist, you can go over the joist inside the wing wall (the vent needs to be at least 6" above the shower threshold before it turns horizontal) to get into the wall with the existing vent stubdown.

To further comment I'd need a bunch of dimensions: horizontally, measured perpendicular to the face of the wall studs, the location of the joist and of the stack below (for a standard 12" rough-in WC and 1/2" finish wall material at the elevation of the tank, the closet flange will be centered at 12-1/2". And vertically, from the backside of the ceiling wall board below, the location of the top and bottom of the joist and notch.

Cheers, Wayne
 
So yes, we plan on centering the toilet and then building a pony wall that will be 32ish by 45ish inches high extending from that back wall. So basically just use a wye where the vertical vent would extend into that wall and then runs up the back wall and reconnects with the current roof vent in the attic?

Would the horizontal need to be 6in above the toilet or shower drain?
 
Last edited:
So yes, we plan on centering the toilet and then building a pony wall that will be 32ish by 45ish inches high extending from that back wall. So basically just use a wye where the vertical vent would extend into that wall and then runs up the back wall and reconnects with the current roof vent in the attic?
To take a vent off straight up, the IPC allows a san-tee on its back, but a combo is better. Or if you need it to go backwards horizontally a bit, a wye and then a 45.
Would the horizontal need to be 6in above the toilet or shower drain?
6" above the shower flood rim (top of shower threshold). If it ever backed up, it would spill out of the shower before hitting the horizontal portion of the vent.

Cheers, Wayne
 
Ok, playing with it a bit more today I am able to get a wye laying flat in there and then immediately a 45 coming off of it after it passes under the joists. Is this appropriate? If this is, what orientation of the wye should it be. The shower drains from the left to the right.

Option 1IMG_1060 Large.jpeg


Option 2
right.jpeg
 
Ok, playing with it a bit more today I am able to get a wye laying flat in there and then immediately a 45 coming off of it after it passes under the joists. Is this appropriate?
No, not for a dry vent takeoff. The wye would have to be rolled up at least 45 degrees. Or a san-tee rolled up 45 degrees (since you are under the IPC).

Also, the vertical drop from the trap outlet to the vent take off is limited to one trap diameter (2" for a 2" shower trap). If the trap has its u-bend against the backside of the ceiling wallboard below, and you have to drop the trap arm to similarly be against the backside of the ceiling wallboard below, that's too much drop.

I think if the trap is in the joist bay next to the joist bay under the wall, and you don't want to go over the joist, and can't drop the trap so its outlet is below the joist, to get a dry vent into the wall you'd have to drill the joist for the vent, which is not advisable. Better to go over the joist in the wing wall between the shower and the WC, or to change the shower pan so the shower drain can drop into the joist bay under the wall.

As to which way to flip the wye, if water got in the vent, you want to direct it to drain downstream, not back towards the shower.

Cheers, Wayne
 
Ok that makes sense. Just seeing all of my option. One last option I would and then I will move forward. What if I rotated it 45 on this side of the joist and then ran a pipe back to the left wall and then a 90 so the vent could run vertically. I could reconnect in the attic. Thanks again for the thoughts!

IMG_1067 Large.jpeg
 
What if I rotated it 45 on this side of the joist and then ran a pipe back to the left wall
Dry vents may not turn horizontal until at least 6" above the fixture (shower) flood rim (threshold). So in particular, no horizontal dry vents below the floor.

Now, for a wet vent, it would fine. E.g. if the lavatory is against that left hand wall, and you ran the lavatory drain to the right (within the wall or through the joists) to connect up to the pipe run you proposed, that would wet vent the shower. The existing dry vent through the roof for the lavatory would be all you need, no requirement to provide a separate dry vent for the shower or WC. And the wye where the lav drain joins the shower would no longer need to be rolled 45 degrees above horizontal, it could be "flat" (2%) or rolled any amount you like.

Cheers, Wayne
 
we used to commonly roll a wye up and run the vent horrizontally with 1/4 inch per foot fall over to the nearest wall and 90 up with the vent up the wall Im in UPC code its generally almost never really legal any more in UPC I think a inspector could be withen his authority to allow in my code or he could deny the installation I would entertain the practice in a jam probebly not with inspection but photo in post 15 was a common sntallation in the 90s in so cal new house construction.
Issue I see is drain is so low the trap is going to be below the cieling below
 