Plumbing Layout. Feedback appreciated

Which of these 3 layouts would you chose? (California IPC)

  • A

    Votes: 0 0.0%
  • B

    Votes: 0 0.0%
  • C

    Votes: 0 0.0%

  • Total voters
    0

Users who are viewing this thread

CaliforniaPlumber

New Member
Messages
8
Reaction score
0
Points
1
Location
San Diego, CA
plumbing2.png
 
Last edited:

wwhitney

In the Trades
Messages
6,560
Reaction score
1,843
Points
113
Location
Berkeley, CA
None of them comply with the UPC, which California uses.

What would comply is putting the 2" dry vent on the shower trap arm, within 5' horizontally and 2" of fall of the shower trap outlet. And then downstream of the vent joining the shower trap arm to the WC drain with a wye that is within 6' along the pipe from the closet flange.

Cheers, Wayne
 

CaliforniaPlumber

New Member
Messages
8
Reaction score
0
Points
1
Location
San Diego, CA
None of them comply with the UPC, which California uses.

What would comply is putting the 2" dry vent on the shower trap arm, within 5' horizontally and 2" of fall of the shower trap outlet. And then downstream of the vent joining the shower trap arm to the WC drain with a wye that is within 6' along the pipe from the closet flange.

Cheers, Wayne
Thanks for the feedback Wayne. I updated my design with your comments
 