New Jersey - Bathroom Plumbing Layout Advice

HeavyJ

New Member
Messages
1
Reaction score
0
Points
1
Location
New Jersey
Hi All,

I'm finishing my basement and preparing my bathroom plumbing. The house was built with rough plumbing for a bathroom but it was 50 years ago and the layout allowed only a narrow shower. We decided that the toilet riser needs to be moved about a foot to the left in order to widen the shower.

What you see in the pick is the 3'x3' hole I broke with the existing layout dug up. I have the 4" toilet drain, 2" shower pipe and the lav waste/wet vent coming from the wall which is a 3" CI below the clean out.

Before breaking the concrete, I assumed the main drain was routed from below the cleanout at a 90 towards the main sewer exit which is 30ft behind me (bottom of the pic), and I would be able to just stack the new toilet riser on top of the existing drain. However, it ended up going to the left towards what I guess is a main pipe that goes down the centerline of the house.

Now my problem is that if I want to plumb this correctly, I understand it has to be ordered wet vent > shower > toilet > sewer main in order to pass nj plumbing code. The issue is if I stack 3 fittings starting at the wet vent, I am way too far to the left with my toilet riser. I need the toilet flange to be roughly in line with the clean out (+- 2").

I was looking for a fitting like a double wye that can pick up the 3" wet vent and 2" shower together but there is no such specific fitting and also AI flagged it as not up to code since the double wye connections will allow waste water to go upstream in the opposite pipe.

What advice can I get to solve this problem? Preferably with the least amount of heavy demo if possible.

Much appreciated in advance!
 

Attachments

  • IMG_1236.jpg
    IMG_1236.jpg
    164.3 KB · Views: 0
New Jersey uses the NSPC, which is much less common than the IPC or UPC, so I am not as familiar with it. But reading the NSPC section on wet venting, I'm not finding any direct statement that the WC has to be the downstream-most fixture on the wet vent.

In fact, the 2021 NJ plumbing code (the latest version 2024 is not available on up.codes) says in 12.10.1(a)(5) "A horizontal branch serving the lavatory and the bathtub or shower stall shall connect to the stack at the same level as the water closet, or it may connect to the water closet bend, or the lavatory and bathtub or shower stall may individually connect to the water closet bend." [I believe "connect to the water closet bend" here means connect to a drain on the the outlet side of it, rather than literally connecting to the bend itself.] For the last bit about "individually connecting" there is no specification in that sentence about the order of connection, suggesting it's fine to have the order going downstream from the WC of "WC - lav - shower". [And most plumbing codes would require that order when the lav has the only dry vent, as at most one wet vented fixture is allowed upstream of the dry vented fixture.]

Having said that, starting at the wall, I believe the branch drain (assuming it is 3", see below if 4") exiting to the left of the picture is far enough from the wall you can plumb the fixtures easily in either order starting from the lav, i.e. (a) lav-WC-shower or (b) lav-shower-WC. Namely, starting in the wall and going downstream, you canb have 3" cleanout - 3" LT90 with outlet horizontal pointing 45 from the wall to the left - (for (b), 3x3x2 wye with branch inlet parallel to the wall to receive the shower) - enter branch inlet of 3" wye with barrel parallel to wall, with WC coming in straight inlet - (for (a), 3x3x2 wye with barrel parallel to wall, branch inlet away from wall and receiving shower).

As you need the barrel of the 3" wye to line up with the existing branch drain, i.e. it needs to be a precise distance from the wall, for option (b) you will likely have to use 1 or 2 street fitting to avoid the wye being pushed too far away from the wall. Worst case you'd need to shift the 3" wye for the WC so that its barrel is parallel to the wall and the branch inlet faces away from the wall. Then the WC closet bend horizontal outlet would point 45 degrees away from the wall to the left; then hit one 45 to turn parallel to the wall, and another 45 to enter that 3" wye branch inlet.

Now if the existing branch drain is 4", you can either do all your replacement work in 3" as above; or if the cleanout needs to be 4", so that you have to have a 4" line from the wall to the branch drain, I think the first option for (b) won't fit (might fit will all street fittings), and you'll have to use the second option.

So depending on those variables, you may have to open the concrete more to the left and/or towards the wall.

Cheers, Wayne
 