Navien NPE-240s - Constant Temp Fluctuations

aeneas01

New Member
Messages
1
Reaction score
0
Points
1
Location
northern california
recently moved into a new home (that was used only as a vacation home, occupied mostly on weekends, about two weekends a month) - it came equipped with a navien npe-240s (no internal recirc pump and no after market exterior recirc pump added) that was installed 6 years ago, the interior of the heater is immaculate, looks brand new, unfortunately faucet and shower temps constantly fluctuate up and down every 30 secs or so, from very hot hot to luke warm, hoping to get to the bottom of this!

what i've done in an attempt to fix the issue:

- thoroughly flushed/descaled tank, cycled vinegar for an hour
- all filters were almost completely clean before i flushed/descaled, water inlet filter had a few lime crumbs
- removed flame rod assembly and sanded rods (altho they were already in very good condition), replaced gasket
- replaced flow sensor and o-rings, propeller on top section of replaced sensor seemed worn
- turned dip-switch to on for lp, all other switches in off position (previous owners converted unit to lp but switch was never turned to on)

none of this solved the problem, the unit behaves exactly as it did before i did the above.

other info:

- water in our area is soft
- tested with multiple faucets turned on, water temp still fluctuates
- water temp is set to 120 on the navien, however the navien info panel shows the out water reaching temps of 140+ when hot water is turned to max, is this normal?

----------------

here's a short vid of the navien with the closest water faucet turned on at max hot and max pressure/volume, the water out reads 0.8 gpm.

at 94f the burners turn on and the temp starts to quickly rise until temp reaches 149f, this takes about 23 secs, burners then turn off turn off and fan turns on, temp starts to drop quickly until it reaches 94f, fan seems to turn off at at around 110f, this takes about another 23 secs, then the cycle starts again and repeats until hot water is turned off.

what else can i try? would a factory reset help? and assistance would be greatly appreciated!

 

Old saggy house

New Member
Messages
3
Reaction score
1
Points
3
Location
Wildwood by the sea
The 240s doesn't have a check valve.

There is a mixing valve on the heater in the cabinet just above the hot water outlet

I had similar issues. My mixing valve was also leaking.

I took the mixing valve apart. There are a few o-rings that needed to be cleaned and regreased. There are two parts to the mixing valve. You will see it when you pull it apart.

There is the electronic stepper motor and then there is the valve. When you separate the two you will see that there is a diagram on each. It shows you how open or closed they are from 0 to 340°

You have to zero out the valve and zero out the stepper motor when you put it back together.

On my first try I didn't get them back together right. I was off one tooth. It was clicking so I took it back apart and put it back together. That was 3 months ago.



On both the valve and the stepper motor there is a 0-340°

There's more than one mixing valve on this unit but the one that was causing me problems was the one right above the hot water outlet.
 

Fitter30

Well-Known Member
Messages
5,921
Reaction score
1,239
Points
113
Location
Peace valley missouri
The 240s doesn't have a check valve.

There is a mixing valve on the heater in the cabinet just above the hot water outlet

I had similar issues. My mixing valve was also leaking.

I took the mixing valve apart. There are a few o-rings that needed to be cleaned and regreased. There are two parts to the mixing valve. You will see it when you pull it apart.

There is the electronic stepper motor and then there is the valve. When you separate the two you will see that there is a diagram on each. It shows you how open or closed they are from 0 to 340°

You have to zero out the valve and zero out the stepper motor when you put it back together.

On my first try I didn't get them back together right. I was off one tooth. It was clicking so I took it back apart and put it back together. That was 3 months ago.



On both the valve and the stepper motor there is a 0-340°

There's more than one mixing valve on this unit but the one that was causing me problems was the one right above the hot water outlet.
Never seen a stepper motor for a mixing valve. Usually it a bellow that temp moves it and controls volume. Problem that I've seen with mix valve the cartridge contain passages that get mineral / limed up. Buy a new cartridge to get water flowing and dump the old cartridge in vinegar for a few days to clean it up for a spare. The hight the water temp the heater is putting out the more minerals are being drove out of the water and heater will need to be cleaned more.
 
Last edited:

nicksports321

New Member
Messages
2
Reaction score
0
Points
0
Location
California
I have a Navien NG NPE-240A about 4 years old. Similar issue as yours

I descaled the unit yesterday along with cleaning the air intake filter. Replaced flow sensor and check valve and also replaced the shower faucet cartridge. Then using the sand paper provided by navien I clean up the flame rod. Still having same issue.

Any help will be greatly appreciated. thank you in advance !
 

GReynolds929

Well-Known Member
Messages
806
Reaction score
286
Points
63
Location
WA
It is most likely the water access valve (WAV) or the mixing valve failing. With water running press the diagnostic button and arrow down to E and F. Watch what the valves are doing. One of them most likely needs replaced.
 

Attachments

  • IMG_0118.jpeg
    IMG_0118.jpeg
    49.3 KB · Views: 75
  • IMG_0119.jpeg
    IMG_0119.jpeg
    45.9 KB · Views: 69

Old saggy house

New Member
Messages
3
Reaction score
1
Points
3
Location
Wildwood by the sea
Never seen a stepper motor for a mixing valve. Usually it a bellow that temp moves it and controls volume. Problem that I've seen with mix valve the cartridge contain passages that get mineral / limed up. Buy a new cartridge to get water flowing and dump the old cartridge in vinegar for a few days to clean it up for a spare. The hight the water temp the heater is putting out the more minerals are being drove out of the water and heater will need to be cleaned more.
Here is a picture of the mixing valve and the stepper motor that controls it from the Navien service manual. These mixing valves cause problems. You can go into the settings and disable them. You can also manually disable them if they fail. The picture linked below is to manually disable the mixing valve.
 

Attachments

  • Screenshot_20260105-115829.png
    Screenshot_20260105-115829.png
    122.1 KB · Views: 68
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks