jvasco2010
New Member
Hello,
I have a Navien NCB-210E that has been serving inconsistent DHW temps. The temp is set to 130 F, but the temps while calling climb pretty fast to 160-180 until it calms itself and repeats. If you call for hot water on more than 1 tap, the temp will get to 210 and trigger the auto shut off (error E001). This boiler also has space heating for 3 zones, and all of that works fine.
The unit is 4, maybe 5 years old. I've owned the home for about a year, and unsure if it has ever been serviced. I did service it myself about 6 months ago (Cleaned air filter, dirt trap, inlet water filter -was clean as a whistle), and things were fine up until a few weeks ago.
After some research, I figured if I called a tech, the first thing they would do is flush the heat exchanger - so I got a pump and ran vinegar through it for an hour last night. There was some scaling, but nothing crazy for potentially never being serviced. The issue appears to remain, however.
I noticed the PSI at idle is ~11.4, and it will not change when calling for hot water. I've read I should be seeing it raise to at least 20 during operation. I want to say around when this issue started, we noticed a very slight drop in pressure in the shower, but didn't think much of it until 1-2 months later when the inconsistent temps (and eventually E001 code) were realized a few weeks ago and assuming it's all related.
The flow rate shows 1.8GPM when one of the taps is wide open, so the sensor is apparently working.
Any ideas? I'm happy to give more information, and appreciate any help offered!
I have a Navien NCB-210E that has been serving inconsistent DHW temps. The temp is set to 130 F, but the temps while calling climb pretty fast to 160-180 until it calms itself and repeats. If you call for hot water on more than 1 tap, the temp will get to 210 and trigger the auto shut off (error E001). This boiler also has space heating for 3 zones, and all of that works fine.
The unit is 4, maybe 5 years old. I've owned the home for about a year, and unsure if it has ever been serviced. I did service it myself about 6 months ago (Cleaned air filter, dirt trap, inlet water filter -was clean as a whistle), and things were fine up until a few weeks ago.
After some research, I figured if I called a tech, the first thing they would do is flush the heat exchanger - so I got a pump and ran vinegar through it for an hour last night. There was some scaling, but nothing crazy for potentially never being serviced. The issue appears to remain, however.
I noticed the PSI at idle is ~11.4, and it will not change when calling for hot water. I've read I should be seeing it raise to at least 20 during operation. I want to say around when this issue started, we noticed a very slight drop in pressure in the shower, but didn't think much of it until 1-2 months later when the inconsistent temps (and eventually E001 code) were realized a few weeks ago and assuming it's all related.
The flow rate shows 1.8GPM when one of the taps is wide open, so the sensor is apparently working.
Any ideas? I'm happy to give more information, and appreciate any help offered!