Navien 240A2 internal recirculation question

Users who are viewing this thread

Gman5757

New Member
Messages
1
Reaction score
0
Points
1
Location
NC
I just had a 240A2 installed . Recirculation is off. Is it worth turning it on just using the internal plumbing/1 liter buffer? No external lines etc... Add: I was thinking it could help with the dishwasher that seem to use very little water over a long period of time.
thanks,
 

Breplum

Licensed plumbing contractor
Messages
1,962
Reaction score
795
Points
113
Location
San Francisco Bay Area
Turning internal recirculation on (and adjusting the setting and turning the bypass lever) will mean that as soon as you open a tap, fully hot water will flow out of your water heater from the buffer tank, because the mini tank will be kept on standby hot.
If recirc. is off, then there is a delay. You can see how long the delay is by putting one hand on the Pressure relief pipe and trip the lever. You will save that much water waiting for hot to arrive at distant fixtures.
 