LG Ductless Split Cassette Drain

Users who are viewing this thread

Matthew Haberland

New Member
Messages
4
Reaction score
0
Points
1
Location
Wisconsin
I have installed plenty of ductless split systems, but I have not installed a cassette head before. The insturctions say you cannot pitch the drain up, but the diagrams that they have show differently. I need to run the drain roughly 12-15 inches up before I can start pitching the line due to where the drain is positioned. Anybody have any input on their installs in the past? The instruction manual is awfully vague.
 

Matthew Haberland

New Member
Messages
4
Reaction score
0
Points
1
Location
Wisconsin
LMCN078HV-NG. I did some more searching and I do believe I found the proper way to route all the drains into one larger PVC.
 

Fitter30

Well-Known Member
Messages
4,361
Reaction score
798
Points
113
Location
Peace valley missouri
Cassettes have a drain pump so the riser isn't a problem just be sure to have a little fall in the main drain line they don't want anymore pressure the pump has to fight.
 