There are a couple people working on this project, it’s on leased farm land so the history and depth of the well are unknown.
The question: what is going on when the water stops flowing, line pressure is zero, and the pump is running and pulling 4.3A. *
Background:
Pump: New VEVOR Deep Well Submersible Pump, 1HP 230V/60Hz, 37gpm Flow 207ft Head
Pressure tank: New Water Worker 44gal
Pressure switch: New 20/40. I don’t have the brand in front of me but it was purchased at a local farm supply.
Circuit breaker: New 2-pole 20A
In line pressure gauge: New, unknown manuf.
Old pump: CountyLine, 1HP, 230V/60HZ, 10GPM. Read from the pump label. This pump just flat out quit working. Even applied voltage with pump out of the well and it’s dead. No idea of the age.
2 weeks ago the water level was 129’ below the top of the case. I measured this myself.
The pump is at least 140’ down the well. The actual measurement wasn’t acquired.
I pressurized the new pressure tank to 18psi. I read that’s the procedure for when the pressure switch is a 20/40.
Pipe comes out of the well as 1”, then Ts to the pressure tank with a gauge on the T, then goes to a hose bib, then feeds a stock tank with an inline shut off valve and a float shut off valve near the top of the stock tank.
Running just the hose bib: the entire system functions as designed. Pump has perfect line and load voltage and pulls 5.5A when running. The pressure switch opens at 40psi/pump stops running and the pressure switch closes at 20psi/the pump starts pumping. When I open the hose bib the line water pressure slowly drops from 40 to 30 and stays there. The other day I ran this for just over 1.5hrs and there were no problems.
* Running just the stock tank feed: Starting with the line water pressure at 40psi, I open the stock tank shut off valve and the line water pressure immediately drops to 20psi and the pump starts and is pulling 6.1A. Water comes out of the stock tank float valve for about a minute then stops when the line pressure reads zero. At this time the pressure switch is closed, pump is running, and line/load voltage is perfect. Pump is pulling 4.3A.
Immediately opened the breaker to prevent the pump from burning up. Wait 5 mins, close breaker and water starts flowing for about 30 secs. then stops. Do it again but wait 10 mins and water flows for about a minute, then stops.
My SWAG because I'm not a plumber: the stock tank float valve has a greater demand than the hose bib, and the water level in the well drops and/or the well can’t provide enough water to meet the pump’s demand, so the pump runs dry.
Thank you.
The question: what is going on when the water stops flowing, line pressure is zero, and the pump is running and pulling 4.3A. *
Background:
Pump: New VEVOR Deep Well Submersible Pump, 1HP 230V/60Hz, 37gpm Flow 207ft Head
Pressure tank: New Water Worker 44gal
Pressure switch: New 20/40. I don’t have the brand in front of me but it was purchased at a local farm supply.
Circuit breaker: New 2-pole 20A
In line pressure gauge: New, unknown manuf.
Old pump: CountyLine, 1HP, 230V/60HZ, 10GPM. Read from the pump label. This pump just flat out quit working. Even applied voltage with pump out of the well and it’s dead. No idea of the age.
2 weeks ago the water level was 129’ below the top of the case. I measured this myself.
The pump is at least 140’ down the well. The actual measurement wasn’t acquired.
I pressurized the new pressure tank to 18psi. I read that’s the procedure for when the pressure switch is a 20/40.
Pipe comes out of the well as 1”, then Ts to the pressure tank with a gauge on the T, then goes to a hose bib, then feeds a stock tank with an inline shut off valve and a float shut off valve near the top of the stock tank.
Running just the hose bib: the entire system functions as designed. Pump has perfect line and load voltage and pulls 5.5A when running. The pressure switch opens at 40psi/pump stops running and the pressure switch closes at 20psi/the pump starts pumping. When I open the hose bib the line water pressure slowly drops from 40 to 30 and stays there. The other day I ran this for just over 1.5hrs and there were no problems.
* Running just the stock tank feed: Starting with the line water pressure at 40psi, I open the stock tank shut off valve and the line water pressure immediately drops to 20psi and the pump starts and is pulling 6.1A. Water comes out of the stock tank float valve for about a minute then stops when the line pressure reads zero. At this time the pressure switch is closed, pump is running, and line/load voltage is perfect. Pump is pulling 4.3A.
Immediately opened the breaker to prevent the pump from burning up. Wait 5 mins, close breaker and water starts flowing for about 30 secs. then stops. Do it again but wait 10 mins and water flows for about a minute, then stops.
My SWAG because I'm not a plumber: the stock tank float valve has a greater demand than the hose bib, and the water level in the well drops and/or the well can’t provide enough water to meet the pump’s demand, so the pump runs dry.
Thank you.