Is a Ell Vent in bathroom set up allowed ?

Dexie

New Member
Messages
4
Reaction score
0
Points
1
Location
62568
I am remastering the layout and adding new components in my master bath. The current layout has the vent on the shower and it provides venting for the entire bathroom. shower, toilet, sink. In the new layout the sink will be using the drain for the old shower. A new tub and shower will sit back to back near the drain for the old sink. The toilet will not move, in the new layout it sits back to back with the sink instead of the shower.
The new shower and tub will be using 2" drains and will connect directly to the main 3" sewer line before the toilet and sink. I want to put in a vent for the tub and shower. (It is a walk in tub with dual drains and I want it to drain rapidly). Can I make this vent in the theory of the ell vent used for islands in a kitchen? I would come off both drains (shower and tub) with a 1 1/2" line up into the wall about 4ft and do a closed "loop", each side connected to the shower and tub drains with a Y connection. Will this accomplish the venting needed ? or will I need to connect all the way back to the wet stack ? The drains and traps are located in a crawl space beneath the floor. I added drawings, hope they are helpful.
 

Attachments

  • close up behind tub shower.jpeg
    close up behind tub shower.jpeg
    57.7 KB · Views: 0
  • new layout.jpeg
    new layout.jpeg
    59.2 KB · Views: 0
  • old layout masterbath.jpeg
    old layout masterbath.jpeg
    59 KB · Views: 0
  • wet vent house layout.jpg
    wet vent house layout.jpg
    67.5 KB · Views: 0
Shower cannot wet vent the bathroom sink. A lavatory (bathroom sink) can wet vent a shower.
 
Your proposed closed loop between two drains is never a vent.

Illinois has its own plumbing code, the venting portion of which is here: https://up.codes/viewer/illinois/il-plumbing-code/chapter/K/vents-and-venting#K

Unlike the IPC, from a quick glance at the above code, Illinois does not allow a dry vented lav to wet vent a WC and both a tub or shower. So you will need to provide two dry vents. There also appears to be no allowance for AAVs.

Your lav will need a dry vent, and then the lav may wet vent the WC. With the drain connectivity you've drawn, you will need to provide a dry vent for the tub/shower branch. It could be downstream of the point where the two drains connect, in which case it would be common venting, and when you check the trap to vent distance for each fixture, you would simply ignore the other fixture. Or it could connect to one fixture drain before the two fixture drains join, which would be wet venting, and for the other fixture you would measure the trap to vent distance to that point of connection of the two fixture drains.

The lav would also be allowed to wet vent one of the tub or shower, so instead of combining the two, you could join one directly to the 3" line (assuming the resulting distance from the trap to that connection complies), and then dry vent the other fixture drain separately and connect it to the 3" line downstream of the 3 other fixtures.

As to the trap to vent distances allowed, see the above link. Another rule that always applies is that the total fall from the trap to the vent connection may not be more than one trap diameter. This is based on the physics of the vent being able to do its job, which is to prevent the possibility of siphoning the trap. That fall limit implies a length limit given the minimum 1/4" per foot fall; but some plumbing codes impose an additional shorter limit.

Cheers, Wayne
 
If you find appendix K illustrations, they do show a lav wet venting a tub/shower and a toilet, but the examples had the toilet downstream.

Most K illustration pages did knot actually show the illustrations.

 
If you find appendix K illustrations, they do show a lav wet venting a tub/shower and a toilet, but the examples had the toilet downstream.
The link you provided is the illustration for 890.1500(g), which covers two bathroom groups back to back, each group having one tub or one shower. It would not apply to single bathroom with a lav, a WC, a tub, and a separate shower.

Cheers, Wayne
 
I will admit that I extrapolated. But bathroom wet venting was a subset of the illustration I did locate.

Still, I have confidence that wet venting via the lav has to be allowed, and the main questions would be must the toilet be last (as in UPC) and what size pipes are big enough for the wet venting. Not allowing horizontal wet venting for a bathroom would be notorious.
 
Not allowing horizontal wet venting for a bathroom would be notorious.
It is allowed, it is just limited to three fixtures: a lav, a WC, and your choice of tub, shower, or floor drain. See 890.1500(f) of Subpart K (Vents and Venting)

Cheers, Wayne
 
Shower cannot wet vent the bathroom sink. A lavatory (bathroom sink) can wet vent a shower.
not understanding this reply. Where am i saying that a shower can wet vent a sink or vice versa ? I am sorry if I wasnt clear in my description. I meant the NEW SINK will sit in the place of the OLD SHOWER and use that drain set up. Hope that helps clear any miscommunication. Thank you for your comment it is appreciated.
 
I did not explain things very well. The original layout was vented and the toilet is at the end of the line. There is a vent before the toilet coming off the old shower with a Y and the vent travels through the attic and attaches at the top of the stack before it exits the house. The new shower and tub has changed and instead of the one 3" pipe being shared each drain will be 2" and run back to connect to the 3" main sewer line. (about 5 ft) there will be a Y on each drain to vent. I have existing 2" lines that can be used so no need to run a new 3" line. The question was could these two vents go up 5' and make a loop without an AAV. I guess I knew the answer before I asked it, I will just make the loop and extend it up into attic and connect to the top stack. I saw this ell vent set up in a kitchen and wondered if I went up high enough if it would work, logic tells me that the air needs somewhere to go so i m not sure how it would work in a kitchen either. Thank you all for your comments and links. Will this be a better layout ?
 
this is how everything was vented, going back and attaching at the main stack. I do not have an upper level as depicted, the picture is just for reference. I have a single story ranch home on a crawl.
 

Attachments

  • Back-Venting.jpg
    Back-Venting.jpg
    41 KB · Views: 0