Apologies in advance for a long post. Want to be thorough here to be sure all needed information is included.
Have an issue that is challenging my normally solid troubleshooting skills. Setup is a restaurant space with hot water run direct from heater to dishwashing sinks and equipment, and all other fixtures (hand sinks, bathrooms, etc.) fed via a Symmons 7-400 thermostatic mixing valve, and there is a hot water recirc loop present. Connections for all this are done to the diagram (diagram #2) shown in the Symmons install manual for the 7-400, with all specified one way checks and ball valves present. Only suggested item not present is a second thermometer on the recirc return line. Cold supply pressure is set via PRV at 75 lbs, and an inline gauge indicates this is holding steady.
This install was done by others, I was contacted to address a lack of hot water pressure and temperature. This is an existing space about 40 years old, and has been refitted numerous times for different restaurant tenants, resulting in a patchwork of abandoned and rerouted lines that confuse the issue and make tracing difficult
Initial customer complaint was almost no hot pressure anywhere but at dishwashing station. Tempering valve was badly scaled up, disassembled and cleaned, reassembled with new factory case seal and sleeve o-ring kit. Full pressure was thus restored to all affected fixtures. However, water runs hot for only 10-15 seconds at any fixture then falls back to cool - less than lukewarm, but slightly warmer than the cold supply - and remains that way unless the faucet is turned off and some time allowed to pass before opening the hot again, in which case the process repeats.
Thermometer on outgoing line from the 7-400 holds generally steady at 110° as was previously set, and that (outgoing tempered hot) line is hot to the touch. The recirc pump has power and is running (sounds normal, have not verified impeller is intact as yet) but the return line at the ingoing side of the recirc pump is cool to the touch, essentially ambient room temperature, as though there is no flow.
The recirc line ties back into the cold supply to the heater and mixing valve past an inline check valve and a ball valve that was placed (per suggested installation diagram) to "fine tune" the amount of water from the return being fed back to the 7-400. I suspect this ball valve may be bad, as it turns a full 90° stop to stop but doesn't feel right, as though it was internally scaled up and forced at some point damaging the seal.
The short explanation of the current problem is that after an initial 10-15 seconds of decent hot water at any fixture fed from the mixing valve, it drops off to just barely warmer than the cold water, as though there is cold water being back fed into the hot side after the mixing valve, and the return never gets hot or even warm to the touch. Pressure to the fixtures remains constant (and good, equal to cold pressure) irrespective of the temperature.
Disassembly is a challenge here due to a tight installation and very close proximity to several electrical load centers, making it a concern to have any water spraying in the vicinity. Any suggestions on whether I should suspect a bad recirc pump/volute blockage, or something else entirely.
I'd add all water lines are run above the ceiling, so the recirc line should theoretically operate at least partly by gravity even if the pump is inoperative, barring a full blockage. I've also considered there may be an inline valve on the recirc line hidden somewhere above the drop ceiling that is closed for reasons not known to me. If that is the case, I'll be spending a lot of time on a ladder popping ceiling tiles trying to find it. It is acting like there is a cross connect present, but so far I've not located any specific fixture or piece of equipment that would be causing that.
Hoping someone here will have encountered a similar problem and can make a suggestion that will reduce the diagnostic time required and avoid a wild goose chase. Appreciate any and all input.
Have an issue that is challenging my normally solid troubleshooting skills. Setup is a restaurant space with hot water run direct from heater to dishwashing sinks and equipment, and all other fixtures (hand sinks, bathrooms, etc.) fed via a Symmons 7-400 thermostatic mixing valve, and there is a hot water recirc loop present. Connections for all this are done to the diagram (diagram #2) shown in the Symmons install manual for the 7-400, with all specified one way checks and ball valves present. Only suggested item not present is a second thermometer on the recirc return line. Cold supply pressure is set via PRV at 75 lbs, and an inline gauge indicates this is holding steady.
This install was done by others, I was contacted to address a lack of hot water pressure and temperature. This is an existing space about 40 years old, and has been refitted numerous times for different restaurant tenants, resulting in a patchwork of abandoned and rerouted lines that confuse the issue and make tracing difficult
Initial customer complaint was almost no hot pressure anywhere but at dishwashing station. Tempering valve was badly scaled up, disassembled and cleaned, reassembled with new factory case seal and sleeve o-ring kit. Full pressure was thus restored to all affected fixtures. However, water runs hot for only 10-15 seconds at any fixture then falls back to cool - less than lukewarm, but slightly warmer than the cold supply - and remains that way unless the faucet is turned off and some time allowed to pass before opening the hot again, in which case the process repeats.
Thermometer on outgoing line from the 7-400 holds generally steady at 110° as was previously set, and that (outgoing tempered hot) line is hot to the touch. The recirc pump has power and is running (sounds normal, have not verified impeller is intact as yet) but the return line at the ingoing side of the recirc pump is cool to the touch, essentially ambient room temperature, as though there is no flow.
The recirc line ties back into the cold supply to the heater and mixing valve past an inline check valve and a ball valve that was placed (per suggested installation diagram) to "fine tune" the amount of water from the return being fed back to the 7-400. I suspect this ball valve may be bad, as it turns a full 90° stop to stop but doesn't feel right, as though it was internally scaled up and forced at some point damaging the seal.
The short explanation of the current problem is that after an initial 10-15 seconds of decent hot water at any fixture fed from the mixing valve, it drops off to just barely warmer than the cold water, as though there is cold water being back fed into the hot side after the mixing valve, and the return never gets hot or even warm to the touch. Pressure to the fixtures remains constant (and good, equal to cold pressure) irrespective of the temperature.
Disassembly is a challenge here due to a tight installation and very close proximity to several electrical load centers, making it a concern to have any water spraying in the vicinity. Any suggestions on whether I should suspect a bad recirc pump/volute blockage, or something else entirely.
I'd add all water lines are run above the ceiling, so the recirc line should theoretically operate at least partly by gravity even if the pump is inoperative, barring a full blockage. I've also considered there may be an inline valve on the recirc line hidden somewhere above the drop ceiling that is closed for reasons not known to me. If that is the case, I'll be spending a lot of time on a ladder popping ceiling tiles trying to find it. It is acting like there is a cross connect present, but so far I've not located any specific fixture or piece of equipment that would be causing that.
Hoping someone here will have encountered a similar problem and can make a suggestion that will reduce the diagnostic time required and avoid a wild goose chase. Appreciate any and all input.