Thanks for the opportunity to post this question here!
In 2022 I installed a 14kw Generac standby -plumber installed a 1.25" poly gas line 40 feet with two risers and full port valves on each end, it passed pressure tests, instapection and we put the generator into service. About 6 mos or so later I noted the rpm's not perfectly smooth at weekly exercise and didn't pay much attention until it seemed to get slightly worse. The condition was (and remains) very similar to what a gas engine sounds like when you've rebuilt the carb and don't have the fuel mixture screw adjusted just right -sounds like it's trying to find a bit more fuel, aka "hunting", aka "surging". Many would not hear the condition, me and all the Generac techs that have tried to remedy it can hear it very well. Condition doesn't change under load.
Generac techs and Generac decided it was a cylinder head issue and replaced the engine under warranty. No change.
Same techs were told to replace lifters (hydraulic) on the new engine. No change.
New tech swapped a new control board, updated software, swapped air filter, onboard regulator, stepper motor. No change.
Gas pressure at the genset is still within specs 7 WC at rest and 6.5 WC at idle. Gas utility came out this week to verify gas pressure and possible contamination. He measured 4oz pressure and after purging the air he showed me the gas analyzer readings were 100% purity at the genset, at my gas range and at my water heater.
Generac techs say it HAS TO BE A GAS ISSUE.
Gas utility tech says GAS SYSTEM INTEGRITY IS 100%, NO LEAKS, PERFECT PRESSURE
My questions for you gas line gurus is this: Is there any remote possibility that my underground gas line can pull in enough air (or moisture) that could cause my generator to not run properly, yet still pass all of the tests per above? Should we go to the trouble of breaking the line loose from the meter and generator and pressure testing it like we did when we 1st installed it?
Thanks,
Mike
In 2022 I installed a 14kw Generac standby -plumber installed a 1.25" poly gas line 40 feet with two risers and full port valves on each end, it passed pressure tests, instapection and we put the generator into service. About 6 mos or so later I noted the rpm's not perfectly smooth at weekly exercise and didn't pay much attention until it seemed to get slightly worse. The condition was (and remains) very similar to what a gas engine sounds like when you've rebuilt the carb and don't have the fuel mixture screw adjusted just right -sounds like it's trying to find a bit more fuel, aka "hunting", aka "surging". Many would not hear the condition, me and all the Generac techs that have tried to remedy it can hear it very well. Condition doesn't change under load.
Generac techs and Generac decided it was a cylinder head issue and replaced the engine under warranty. No change.
Same techs were told to replace lifters (hydraulic) on the new engine. No change.
New tech swapped a new control board, updated software, swapped air filter, onboard regulator, stepper motor. No change.
Gas pressure at the genset is still within specs 7 WC at rest and 6.5 WC at idle. Gas utility came out this week to verify gas pressure and possible contamination. He measured 4oz pressure and after purging the air he showed me the gas analyzer readings were 100% purity at the genset, at my gas range and at my water heater.
Generac techs say it HAS TO BE A GAS ISSUE.
Gas utility tech says GAS SYSTEM INTEGRITY IS 100%, NO LEAKS, PERFECT PRESSURE
My questions for you gas line gurus is this: Is there any remote possibility that my underground gas line can pull in enough air (or moisture) that could cause my generator to not run properly, yet still pass all of the tests per above? Should we go to the trouble of breaking the line loose from the meter and generator and pressure testing it like we did when we 1st installed it?
Thanks,